derate Q #80866
06/09/02 01:31 PM
06/09/02 01:31 PM
E
Eandrew  Offline OP
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
If a conductor is for a continuous load and feeds the load through a raceway of more than three conductor, do you only apply the fill correction and forget the continuous load aspect. Or do you take them both into consideration?

2017 / 2014 NEC & Related Books and Study Guides
Re: derate Q #80867
06/11/02 03:54 PM
06/11/02 03:54 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
You must use the derating for continous
load and conduit fill when derating these conductors.

Re: derate Q #80868
06/11/02 05:29 PM
06/11/02 05:29 PM
E
Eandrew  Offline OP
Member
Joined: May 2002
Posts: 68
seattle, wa, usa
Thanks Bob.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,503
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,682 Are you busy
186,422 Re: Forum
175,902 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9496 MB (Peak: 1.0745 MB) Zlib enabled. Server Time: 2018-08-21 19:37:37 UTC