If a conductor is for a continuous load and feeds the load through a raceway of more than three conductor, do you only apply the fill correction and forget the continuous load aspect. Or do you take them both into consideration?

Work Gear for Electricians and the Trades

Workgear for Electricians

#80867 06/11/02 03:54 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
You must use the derating for continous
load and conduit fill when derating these conductors.

#80868 06/11/02 05:29 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
Thanks Bob.