#80804 05/23/02 10:03 PM
Joined: May 2002
Posts: 5
Z
Zapper Offline OP
Junior Member
680.70 does not say any thing about a disconnect for the tub motor-Does the code say a discoonect is need such as a toggol switch - 20amp 125v. on the bathroom wall for the motor??

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#80805 05/26/02 05:51 AM
Joined: Oct 2000
Posts: 5,392
S
Member
Zapper;
part VII blows off the rest of 680....

VII. Hydromassage Bathtubs
680.70 General.

Hydromassage bathtubs as defined in 680.2 shall comply with Part VII of this article. They shall not be required to comply with other parts of this article.

while asking to comply with chap's 1-4..

680.72 Other Electrical Equipment.
Luminaires (lighting fixtures), switches, receptacles, and other electrical equipment located in the same room, and not directly associated with a hydromassage bathtub, shall be installed in accordance with the requirements of Chapters 1 through 4 in this Code covering the installation of that equipment in bathrooms.

which would bring us to 430 & disco's, right?

[Linked Image]
???

#80806 05/27/02 07:06 AM
Joined: Jan 2002
Posts: 1,457
E
Member
In my experience no switch is needed. They are cord and plug connected so that covers your disconnect. I do usually install one anyway. Just seems like good safety practice. Also some manufacturers instructions suggest that you provide a safety switch.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
BigB 8
triple 3
Popular Topics(Views)
302,620 Are you busy
231,935 Re: Forum
216,579 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5