Exactly what taps are being referred to in Table 210.14. that are allowed to tap #14 to a 20 amp ckt? Fixture taps?

The question came up about running a 20 amp ckt. for DW/GD and running 2 #14-2s to the loads.

I don't go for it.

Horizontal Ad
#80596 05/02/02 07:00 PM
Joined: Oct 2000
Posts: 5,393
S
Member
Redsy,
where is this in the 02' [Linked Image]

#80597 05/02/02 08:42 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Redsy,
I think that you are referring to Table 210.24. The only applications that I know of are in the exception to 210.19(A)(4). It appears that if you hardwired the dishwasher and the garbage disposal, and the combined loads did not exceed 20 amps and the #14 tap conductors did not exceed 18", that the installation would be code compliant.
Don(resqcapt19)


Don(resqcapt19)
#80598 05/02/02 09:36 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Thanks, Don. I think I'd skip this attempt at saving about $.03.
sparky, Don was right, I meant table 210.24.


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Admin
Admin
NY, USA
Posts: 3,672
Joined: October 2000
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
557,452 Are you busy
432,069 Re: Forum
401,340 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5