ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Where is Everyone?
by luckyshadow - 11/21/21 10:14 AM
It's been an interesting career
by The Watt Doctor - 11/19/21 09:56 AM
Well I am back to stay (nearly 6 years)
by The Watt Doctor - 11/19/21 09:17 AM
Motor Load Relationships Between Fans and Pumps
by The Watt Doctor - 11/18/21 09:24 AM
GFCI's pops in large numbers
by dsk - 11/05/21 06:45 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 32 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Apr 2002
Posts: 178
R
Member
Yesterday we went to a plant where some conductors melted in the conduit.There was several problems all the circuits were over loaded #12`s 20+ amps about 19 8' floresant on each cir.They have 1 1/4 conduit with 36 # 12 conductors all over loaded and the conduit is very hot.The question I have how best to explain to the electrical poeple How to size the number of circuits in a pipe.The code table c8 says they can have 45 in the pipe but I tried explaining that with the ciruits over loaded and the heat generated the fill and current carrying capasity of the wires would be less.I don`t think I did a good job with them understanding so please help us out with some examples and code articals thanks guys.We ran another 1 1/4 conduit over and that reduced the heat and we split the circuits droping the current to each circuit.

2017 / 2014 NEC & Related Books and Study Guides
Joined: Mar 2001
Posts: 2,056
R
Member
See table 310.15(B)(2)(a) for adjustment factors.
36 conductors require an ampacity adjustment that results in only 40% of the Table 310.16 values.
In your case (using the 90c column for derating purposes) .4 x 30 amps = 12 amps for #12 copper.

Joined: Jan 2001
Posts: 75
G
Member
Is that 36 ungrounded conductors plus neutrals ?

Many plants have 3Ø 4W so the neutrals would be current carrying also on circuits with ballasts.

If so, could be 35 percent derate.
30A * 0.35 = 10.5 Ampacity.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
286,175 Are you busy
218,629 Re: Forum
204,822 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5