Arc Fault Brkrs& Ltng #80413
04/10/02 06:51 PM
04/10/02 06:51 PM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
hi,
this is a double barrell question.

1.)can you feed the required outlet for HVAC maint from the same circuit that feeds a bedroom? The circuit is arc fault protected.

2.) can you feed the light in the bathroom and the light in the laundry room from the bathroom circuit? I know the laundry circuit itself can only have a built in appliance like an iron on it...nothing else and has loading restrictions..80% i think...

vent/light combo only no heat.

thanks for any replies

frodo

2017 / 2014 NEC & Related Books and Study Guides
Re: Arc Fault Brkrs& Ltng #80414
04/10/02 08:18 PM
04/10/02 08:18 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Frodo,
For the bathroom recept you must feed it with a 20 amp circuit. This can feed all the bath gfis,or just one bath gfi, or one bath gfi and other lights or such in that same bath only.

Re: Arc Fault Brkrs& Ltng #80415
04/11/02 07:28 AM
04/11/02 07:28 AM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
hi,
i was reading the code and its says that a receptacle must be located in the bathroom but i didnt read anything that says you cant attach any other outlets?

thanks

frodo

Re: Arc Fault Brkrs& Ltng #80416
04/11/02 08:18 AM
04/11/02 08:18 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
210-11(c))(3)

Read closely the last sentence and the exception.

Such circuits shall have no other outlets.

Ex. Where a 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with section 210-23(a).


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Arc Fault Brkrs& Ltng #80417
04/11/02 08:25 AM
04/11/02 08:25 AM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
hi,
you guys are fast...i found the article and couldnt make it back to the comp before i got nailed...my memory is getting very bad...


got it..

thanks

frodo

Re: Arc Fault Brkrs& Ltng #80418
04/17/02 09:42 AM
04/17/02 09:42 AM
C
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
hi frodo, the answer to the 1st question is that there isnt anything that requires an hvac servicing receptacle from being on a specific circuit and nothing that limits an afci circuit to a bedroom, if that was the question


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,121 Are you busy
189,133 Re: Forum
178,803 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.008s) Memory: 0.9759 MB (Peak: 1.1230 MB) Zlib enabled. Server Time: 2018-12-10 06:23:44 UTC