Service-Entrance Conductors #80408 04/09/02 11:13 PM
Joined: Jan 2002
Posts: 21
M
MVillines Offline OP
Member
Can the grounded conductor at the service head (service point) be identified by stripping the insulation off the conductor as described in section 250.114 or must it be identified per section 200.6? Article 230 seems to be silent except for section 230.41, which permits the grounded conductor to be bare.

2017 / 2014 NEC & Related Books and Study Guides
Re: Service-Entrance Conductors #80409 04/10/02 12:59 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
No, Article 250 applies to grounding conductors, not grounded conductors. The grounded conductor must be identifed per Article 200.
Don(resqcapt19)


Don(resqcapt19)
Re: Service-Entrance Conductors #80410 04/10/02 10:58 PM
Joined: Jan 2002
Posts: 21
M
MVillines Offline OP
Member
Don
If you identify the grounded service-conductor per Article 200, that would mean you would have to mark the bare grounded conductor with paint or tape if the conductor is larger than 6 AWG. If the conductor is #6 AWG or smaller the identification would have to continuous the entire length of the conductor. This would conflict with section 230.41 that permits the conductor to be bare. What would an electrician say about the inspector that required white tape or paint on the bare conductor?

Re: Service-Entrance Conductors #80411 04/11/02 07:58 AM
Joined: Jun 2001
Posts: 642
N
nesparky Offline
Member
local poco requires grounded conductor to be stripped 6" from weatherhead. Will not accept tape or paint- call those methods not permenant.
Different local rules in other poco areas do apply.


ed
Re: Service-Entrance Conductors #80412 04/11/02 10:58 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
MVillines,
The original question asked about striping the end of an insulated conductor to identify it as a grounded conductor. While 230.41 does permit the use of a bare conductor as a grounded conductor, it does not permit you to strip the end of an insulated conductor to identify it as the grounded conductor. If the grounded conductor is an insulated conductor the code requires identification per Article 200. Article 200 does not require additional identification of a bare grounded conductor.
Don(resqcapt19)


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,722 Are you busy
204,962 Re: Forum
193,067 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3