#80408 04/09/02 10:13 PM
Joined: Jan 2002
Posts: 21
M
Member
Can the grounded conductor at the service head (service point) be identified by stripping the insulation off the conductor as described in section 250.114 or must it be identified per section 200.6? Article 230 seems to be silent except for section 230.41, which permits the grounded conductor to be bare.

2017 / 2014 NEC & Related Books and Study Guides
Joined: Nov 2000
Posts: 2,148
R
Member
No, Article 250 applies to grounding conductors, not grounded conductors. The grounded conductor must be identifed per Article 200.
Don(resqcapt19)


Don(resqcapt19)
Joined: Jan 2002
Posts: 21
M
Member
Don
If you identify the grounded service-conductor per Article 200, that would mean you would have to mark the bare grounded conductor with paint or tape if the conductor is larger than 6 AWG. If the conductor is #6 AWG or smaller the identification would have to continuous the entire length of the conductor. This would conflict with section 230.41 that permits the conductor to be bare. What would an electrician say about the inspector that required white tape or paint on the bare conductor?

Joined: Jun 2001
Posts: 642
N
Member
local poco requires grounded conductor to be stripped 6" from weatherhead. Will not accept tape or paint- call those methods not permenant.
Different local rules in other poco areas do apply.


ed
Joined: Nov 2000
Posts: 2,148
R
Member
MVillines,
The original question asked about striping the end of an insulated conductor to identify it as a grounded conductor. While 230.41 does permit the use of a bare conductor as a grounded conductor, it does not permit you to strip the end of an insulated conductor to identify it as the grounded conductor. If the grounded conductor is an insulated conductor the code requires identification per Article 200. Article 200 does not require additional identification of a bare grounded conductor.
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Top Posters(30 Days)
dsk 2
NORCAL 1
Popular Topics(Views)
286,557 Are you busy
218,974 Re: Forum
205,093 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5