sub panel to storage building/shop #80401 04/09/02 11:30 AM
Joined: Apr 2002
Posts: 178
R
Reel-Break Offline OP
Member
In wiring a storage building from home panel I`m running 100 amp service to it 4 wire use now I`m not sure do I drive a ground rod or 2 ground rods or does the 4th egc wire take care of it. Thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Re: sub panel to storage building/shop #80402 04/09/02 04:44 PM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
Reel,
99 code 250-32. If your building has more than one ckt (and I'm pretty sure we can assume it does) you have to have a grounding electrode (rod, water pipe, effectively grounded bldg steel, etc.) connected to your green, bare, whatever grounding conductor.

Using 4 conductors, your neutral and ground are kept separate at the out-building service, but the ground must have an electrode.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,069 Are you busy
205,048 Re: Forum
193,177 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3