#80219 03/18/02 11:38 AM
Joined: Mar 2002
Posts: 60
J
Member
Someone told me that a 50 amp. hot tub does not have to be GFI protected. Just bonded with a #6 bond wire to the panel. (Also with a disconnect.) He claims that only 15 and 20 amp. circuits require gfi protection. Being I am not as indebth to the NEC as most of you. [Linked Image] Could someone please tell me if the advice I am given is true..

James

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#80220 03/18/02 01:27 PM
Joined: Dec 2000
Posts: 38
T
Member
James Article 680.22 A (5) (2002 NEC)
"Receptacles that supply pool pump motors and that are rated 15 or 20 amperes, 120 volt through 240 volts, single phase, shall be provided with GFCI protection." It is section II permenatly installed pools but both section 680.42 and 680.43 reference compliance to section I and II.

#80221 03/18/02 04:34 PM
Joined: Mar 2002
Posts: 60
J
Member
There is no recep. its 50 amp. hard wired to the unit. This is whats puzzling me.

#80222 03/18/02 04:36 PM
Joined: Nov 2000
Posts: 2,148
R
Member
I don't think a hot tub is required by the NEC to have GFCI protection if it is hard wired. If it is cord and plug connected, 680.43(A)(4) will require GFCI protection. The listing instructions may also require GFCI protection.
Don(resqcapt19)


Don(resqcapt19)
#80223 03/18/02 05:17 PM
Joined: Nov 2001
Posts: 280
M
Member
Every Hot-tub and Spa I have seen says in the instructions if hard wired use a 50 GFCI breaker, a lot of the units that can run on 120 volts have a gfci built right into the cord.
I wouldn't want to put one in without it being GFCI protected.

_Mark

#80224 03/18/02 05:39 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
This gets a little clearer (I think) in the 2002 code. 680.4 requires compliance with parts I & IV of the article, part IV is the section that deals with hot tubs & spas.

680.42 has some additional wiring requirements for outdoor installations.

680.44 requires GFCI protection. Of course, theres the usual cast of exceptions.

Every hard wired tub I've seen has GFCI protection mandated in the instructions.


Few things are harder to put up with than the annoyance of a good example.
#80225 03/18/02 07:49 PM
Joined: Jan 2002
Posts: 1,457
E
Member
Im not sure of the brand but there is a 50 amp disconnect with built in gfi protection made for hot tubs. I see it at my supply house every day, let me know if you want more info.

#80226 03/18/02 09:22 PM
Joined: Nov 2001
Posts: 280
M
Member
In the code Handbook under 680.44, It says, "The requirements of 680.44 specify that field-assembled Spas and Hot tubs with heater loads of 50 amps or less are to be GFCI protected"
I cannot imagine putting one of these units in without GFCI protection, Lloyds of London wouldnt have that kind of money for the insurances and the lawsuits.
-Mark

#80227 03/18/02 11:36 PM
Joined: Nov 2000
Posts: 2,148
R
Member
motor,
You are correct, 680.44 does require GFCI protection for the hot tub outlet. I missed that.
don


Don(resqcapt19)
#80228 03/19/02 02:17 AM
Joined: Mar 2002
Posts: 60
J
Member
That is what I thought.. Just have to becareful who you take advice from.. [Linked Image] I mean to say many of the older homes here on long island are run on a 60 amp service. So lets take that service and feed a hot tub! It would be stupid not to GFI protect it.. [Linked Image]

James

Page 1 of 3 1 2 3

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,039 Are you busy
233,457 Re: Forum
218,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5