Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
Can, and should a motion controlled switch be used to control illumination of panelboards? What are your thoughts?

Bill


Bill
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Oct 2000
Posts: 2,749
Member
Bill:

I would answer NO, because of the rule in 110.26(D) Illumination last sentence.

Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, or motor control centers installed indoors.

Additional lighting outlets shall not be required where the work space is illuminated by an adjacent light source or as permitted by 210.70(A)(1), Exception No. 1, for switched receptacles.

In electrical equipment rooms, the illumination shall not be controlled by automatic means only.


Joe Tedesco, NEC Consultant
Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
Joe,

Thanks, I would agree about it probably not being a good idea, but (strictly speaking) I don't see this code section prohibiting it for the following reasons;

What if it is not in a separate room?
Does the term 'Automatic' really include Motion-Controlled?
If it is a Motion-Controlled wall switch it also has a manual setting.

Bill


Bill
Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
I was just thinking that maybe I was interpreting the words 'Automatic Means' too literally.

My first thought was that 'Automatic Means' meant something that wastotally under the control of outside forces and that the person in the room had no way of controlling it at all. (This would literally be wrong if the light could be controlled by his movements)


Bill

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,432
Joined: July 2002
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
302,779 Are you busy
231,981 Re: Forum
216,708 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5