#80123 02/28/02 10:33 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is it legal to have a 20a 120v single recepticle outdoor "not GFI protected", for a spa if the spa has its own GFI built into the plug? Does the recept have to be 5 feet away from the spa?


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#80124 02/28/02 10:36 PM
Joined: Oct 2000
Posts: 4,080
Likes: 3
Member
Al,

If the Receptacle is outside it has to be GFCI protected period.

Bill


Bill
#80125 03/01/02 10:07 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Thanks Bill, kinda what I was thinking, that makes sense. Would there be any problem with tripping by putting a GFI recept or breaker in since it would be double GFI protected? (The recept and the spa plug both having a GFI on the same 2a ckt).


The Golden Rule - "The man with the gold makes the rule"
#80126 03/01/02 10:10 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
correction to previous message - "20a ckt"


The Golden Rule - "The man with the gold makes the rule"
#80127 03/01/02 10:38 AM
Joined: Oct 2000
Posts: 4,080
Likes: 3
Member
Al,

I haven't encountered any problems with double GFCI protection like this. These Tubs have been coming with GFI protection in the control panels and some on the cords for years. Look at Hairdryers for a similar situation. Many come with a built-in GFCI (or similar) and don't seem to cause any problems with the Bathroom GFCI.

Bill


Bill
#80128 03/02/02 07:02 PM
Joined: Feb 2002
Posts: 38
H
Member
aldav53
680 !
part VI 680.40 ,,,680.42 then in partII read 680.22(a)(4) that should be enough for ya!


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Trumpy 9
NORCAL 5
Popular Topics(Views)
300,508 Are you busy
230,151 Re: Forum
214,962 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5