0 members (), 286 guests, and 6 robots.
#79851 01/31/02 08:48 PM
Per 210-21(b), would you consider a duplex outlet a single receptacle?
Can a 15 Amp duplex be installed on a 20 Amp circuit without any other outlets?
(I've got somebody that won't believe me)
Workgear for Electricians
#79852 01/31/02 09:10 PM
The FPN refers us to article 100. (Definition of receptacle)
“A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.”
A duplex is a multiple outlet device by definition.
Yes on 15A duplex receptacle can be protected by a 20A breaker.
#79853 02/04/02 09:19 PM
Nick,
I am not sure but if it is a dedicated 20 amp line, you must use a 20amp recp.I could be wrong.
#79854 02/04/02 09:31 PM
Only if it's a 'single' receptacle. A duplex is not a single receptacle by definition.
#79855 02/04/02 10:06 PM
Ditto Nick. A duplex is 2 receptacles and, therefore a 15 amp is acceptable, even on a dedicated line.
#79856 02/06/02 09:03 AM
Thanks, fellers. Although I originally showed the "stuporintendent" the exact same chain that Nick mentioned, he wouldn't agree. I asked you, printed this thread, and brought it in to him. He's now shut up but he's mad [Linked Image]:
#79857 04/17/02 08:47 PM
If you take a duplex, break off the hot and neutral tabs, and feed two circuits into it, would it be considered 2 single outlet circuits? [Linked Image]
#79858 04/17/02 09:47 PM
It still would not meet the definition of a single receptacle because it is still two devices on one yoke.