Interior Service Conductor #79837
01/30/02 08:43 PM
01/30/02 08:43 PM
I
ibuildit4u  Offline OP
Junior Member
Joined: Jan 2002
Posts: 4
burgaw,nc,usa
I have been told that it is a code violation to have an interior breaker panel located more than 3 feet from the exterior meter main even if it is connected to the meter main by a 4 conductor sheathed cable rated at the ampacity of the service main. This propsed cable would enter the house and run through the rafter area and down to the circut panel a distance of 18' ... can anyone give me insight on this issue ???? thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Interior Service Conductor #79838
01/30/02 09:04 PM
01/30/02 09:04 PM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
I don't see that you have a problem. If indeed you have a "meter main", then that is your service, and the rest is a sub-panel..fed by the 2 hots, a neutral,and a ground.
If you are just going from a meter, then several feet to your service..that's where you run into difficulty..depending upon local rules, usually.

Re: Interior Service Conductor #79839
01/30/02 09:15 PM
01/30/02 09:15 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Ditto, elzappr.
Once you leave your service main, it becomes a feeder and you can run as far as you like with it. Without an external main, I would check with local AHJ for anything that exceeds 3 ft.

Re: Interior Service Conductor #79840
01/30/02 09:30 PM
01/30/02 09:30 PM
I
ibuildit4u  Offline OP
Junior Member
Joined: Jan 2002
Posts: 4
burgaw,nc,usa
Thanks for your Rapid Replys .... its is a meter/main ... square D unit with a meter socket and a 200 amp breaker with 6 slots within the same enclosure .. this would be mounted out side the building and connected to an underground service form the power company ... from the load side of the 200 amp main c/p I am running a 200 amp al service cable which has 2 line 1 neutural and 1 bare ground wires all cased in a plastic sheath ... this would exit the meter main enclosure from the rear through the exterior wall of the house up to the overhead attic space across and down to the square d 200 amp 30 circuit panel ... the exterior box is grounded with a ground rod and #4 copper the interior panel is bonded to the bare ground lead of the service cable and neutural .... I dont see any problem with this arrangement ... i will be calling for a REVIEW with the local inspector and wanted to have my facts ... i can find nothing in the nec 2002 codes that would violate this arrangement .... more input is welcomed .... thanks

Re: Interior Service Conductor #79841
01/30/02 10:16 PM
01/30/02 10:16 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Before you ask for that review, check for any local (city or county) and/or state admendments to the NEC. Some cities here have length restrictions on services, and some have a conduit requirement for services and feeders.


ed
Re: Interior Service Conductor #79842
01/30/02 10:28 PM
01/30/02 10:28 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Here, it used to be 25 ft. (WV Power), now it has to be back to back or a disco is required. (Allegheny Power).

My longest distance between disco and panel is about 400 ft. It was at the house with the solar panels/inverter setup. [Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Interior Service Conductor #79843
01/31/02 02:46 AM
01/31/02 02:46 AM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Just to make sure.. You haven't connected the ground and neutral together at the sub-panel did you. I wondered, when you stated that the sub-panel was "bonded to the bare ground lead of the service cable and the neutral."

Re: Interior Service Conductor #79844
01/31/02 04:41 PM
01/31/02 04:41 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
Would this apply?


110.10 Circuit Impedance and Other Characteristics.
The overcurrent protective devices, the total impedance, the component short-circuit current ratings, and other characteristics of the circuit to be protected shall be selected and coordinated to permit the circuit-protective devices used to clear a fault to do so without extensive damage to the electrical components of the circuit. This fault shall be assumed to be either between two or more of the circuit conductors or between any circuit conductor and the grounding conductor or enclosing metal raceway. Listed products applied in accordance with their listing shall be considered to meet the requirements of this section.

Re: Interior Service Conductor #79845
01/31/02 07:56 PM
01/31/02 07:56 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
With a meter/main breaker combo and the conductor protected at its ampacity you can run to Timbuktu. An unprotected conductor can't. It's a feeder after the main, not a service conductor.
Virgil, don't you mean without a main c/b located @ the service?



[This message has been edited by electure (edited 01-31-2002).]

Re: Interior Service Conductor #79846
01/31/02 09:12 PM
01/31/02 09:12 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Yeah, back to back no Disconnect (w/ Main CB), not back to back, must have disco (W/ main CB)...

Did I clear my muddling up a little?

<in jest>(Listen to what I mean, not what I say...)</in jest>

[Linked Image]

The 400 ft run had a Main CB/ Disco adjacent to the meterbase, so technically, it was a "feeder" and not a "service".

Still a long run.

My longest run was 600 ft. of 1/0 Cu for a 240V 30A feed for a cell tower repeater.
That pull was a nightmare... I had used 2" PVC instead of 3" and will never do that again.

[This message has been edited by sparky66wv (edited 01-31-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
KevinL 2
Popular Topics(Views)
251,576 Are you busy
188,729 Re: Forum
178,441 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 1.0260 MB (Peak: 1.2022 MB) Zlib enabled. Server Time: 2018-11-18 20:42:30 UTC