430-7 motor nameplate data #79830 01/30/02 10:57 AM
ctolbert Offline OP
The rated full load speed is always listed on a standard 3-phase induction motor in RPM.
The question is where does one find the maximum rpm possible for a motor? Is it from the manufacturer only? There is no ref. in NEMA mg1 on this particular subject that I remember.
Is it more a function of insulation rating or mechanical transmission I.E. bearing life?
Carl
Carl Lee Tolbert
Technical Support
AC Drives
Automationdirect.com
Your source for the most practical automation products at almost-free pricing, delivered by 11 a.m., just by clicking a mouse.
PH: (770)844-4200
Fax:(770)886-3199
www.automationdirect.com
2017 / 2014 NEC & Related Books and Study Guides
Re: 430-7 motor nameplate data #79831 01/30/02 12:48 PM
Redsy Offline
Are you wondering about the maximum speed that would be allowed if operated by a VFD? Otherwise, how would you increase the speed
(beyond the theoretical speed minus slip?)
Re: 430-7 motor nameplate data #79832 01/30/02 01:23 PM
ctolbert Offline OP
Yes, sorry....If someone wanted to run the max of a 4 pole motor at 3000 rpm.
Carl
Carl Lee Tolbert
Technical Support
AC Drives
PH: (770)844-4200
Fax:(770)886-3199
Re: 430-7 motor nameplate data #79833 01/30/02 04:15 PM
Redsy Offline
What is your application? How big & fancy is the motor? This question came up in one of our drive applications. I couldn't get a firm maximum RPM value from our rep. He said you can overspeed them somewhat, but you lose HP. I would call the motor manufacturer to get an answer. If you are going to regularly operate in the 3000 RPM range, you should probably get a 3600 RPM motor and control that instead.
Re: 430-7 motor nameplate data #79834 01/30/02 04:45 PM
ctolbert Offline OP
It's not a question dealing with a specific application.
Is it something a motor mfg. can only answer (like you said calling the company)?
I was looking for documentation or information that elaborated on the concept of over-driving standard 3 phase motors. With reference to nameplate data and NEC 430.
I really appreciate your help Redsy.
Carl
A friend of mine found the information I was looking for. It was in NEMA MG-1. There is no reference in NEC for this motor information. The image is a screen capture of the appropriate page.
Thanks,
Carl
(picture inserted into thread)
[This message has been edited by Webmaster (edited 01-31-2002).]
Carl Lee Tolbert
Technical Support
AC Drives
PH: (770)844-4200
Fax:(770)886-3199
Re: 430-7 motor nameplate data #79835 01/31/02 11:27 AM
ctolbert Offline OP
12.53.1 is the applicable clause. It's a pain sometimes weeding through the information.
Thanks everyone.
Carl
Carl Lee Tolbert
Technical Support
AC Drives
PH: (770)844-4200
Fax:(770)886-3199
Re: 430-7 motor nameplate data #79836 02/01/02 05:57 PM
Redsy Offline
Carl,
Is the table shown actually 12-4A, or is that shown elsewhere?
[This message has been edited by Redsy (edited 02-01-2002).]