I have been reviewing changes in the 2002 NEC and had a question that I would like to get the Board's input on. Section 404.8(B) notes that if two devices (a snap switch and another device such as a switch or receptacle) are installed in an enclosure and there is greater than 300V potential difference between the adjacent devices, a barrier between the two devices must be installed.

A Code Change book that I was reading then gave an example of a switch (use to switch a 277V lighting circuit) installed next to a 120V receptacle. It indicated that the voltage between the two devices would be greater than 300V (277V + 120V). However if you were to put a voltmeter probe on one of the conductors of the 277V circuit and the other voltmeter lead on a wire from the 120V circuit, the voltmeter would read 0V because the two supplies are isolated from one another. I have read two different "2002 NEC Change" books and they both provide a similar example. What is your take on this?

I could understand that if two, 277V circuits were switched from two switches in one enclosure there would be a potential difference of 480V between the switches assuming that two different phases were used. However I don't interpret 404.8(B) the way that these two Code Change books have.

Horizontal Ad
Joined: Nov 2000
Posts: 2,148
R
Member
You will read voltage becuse the systems are not really isolated. They grounded conductors of both systems will be tied together by the grounding system.
Don(resqcapt19)


Don(resqcapt19)
Joined: Aug 2001
Posts: 7,520
P
Member
With a common neutral/ground the voltage you get between a 277V hot and a 120V hot will depend upon which phase of each system is present. It will certainly exceed 300V in some combinations.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Top Posters(30 Days)
Popular Topics(Views)
337,602 Are you busy
262,962 Re: Forum
243,236 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5