ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Mini Split voltage
by Garemaret - 06/21/24 04:53 AM
Strobing LEDs
by Anovalight - 06/20/24 03:16 AM
Stuff that happens after we leave
by HotLine1 - 06/17/24 03:53 PM
photocell requirement for metal halide ballasts
by gfretwell - 06/17/24 01:44 PM
Commercial lift stations
by triple - 06/09/24 05:23 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 164 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#79386 12/17/01 05:49 PM
A
Anonymous
Unregistered
Recently ran into a dilemma with regards to the proper breaker on a circuit. The simple branch circuit contains a 12-2 w/g feed that has a 14-3 w/g branch from into. Thus creating two circuits from the single 12-2 wire. The debate among elder electricains (who know the code quite well) and inspectors is whether or not the the circuit is to be protected with a 20 amp or a 30 amp fuse. First inclination is that you default to your weakest link and install the 15 amp breaker to protect the 14 gauge wire. However, inspectors in the business for years and some local electricians feel that the circuit can be protected by the 20 amp breaker and meet code. I remember looking this up in the 1996 NEC code and finding support for this. Does anyone have any idea about this? Joe?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#79387 12/17/01 06:16 PM
Joined: Oct 2000
Posts: 2,749
Member
See the *Note under Table 310-16 and Section 240-3. See also Section 110-14(c).


Joe Tedesco, NEC Consultant
#79388 12/17/01 09:02 PM
Joined: Mar 2001
Posts: 2,056
R
Member
15 amp protection. This is similar to installing 15 amp branch ckt. wiring and using #12 for the homerun. It is a 15 amp ckt.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5