NEC 310.15 (B) (2) (a) #79219
12/07/01 01:42 PM
12/07/01 01:42 PM
M
mdsmith  Offline OP
Junior Member
Joined: Dec 2001
Posts: 5
When you install 120V, single phase circuits in a raceway, each with a separate neutral, do you count the neutrals when applying the provisions of 310.15(B)(2)(a)? or does 310.15(B)(4)(a) apply to this situation?

2017 / 2014 NEC & Related Books and Study Guides
Re: NEC 310.15 (B) (2) (a) #79220
12/07/01 02:03 PM
12/07/01 02:03 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Each neutral carries the same current at the associated phase conductor and therefore must be counted as current carrying conductors.
Don(resqcapt19)


Don(resqcapt19)
Re: NEC 310.15 (B) (2) (a) #79221
12/07/01 06:43 PM
12/07/01 06:43 PM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 329
Bruceton Mills, WV
In a word... yes. If you have a shared neutral on a single phase multiwire circuit it would not count.

Re: NEC 310.15 (B) (2) (a) #79222
12/08/01 08:47 AM
12/08/01 08:47 AM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
Steve,

Isn't that on linear loads?

Non-linear loads using a multiwire method ( N-A-B-C ), the neutral is considered a current carrying conductor. 220-22 FPN#2, 310-15(b)(4)(c).

Re: NEC 310.15 (B) (2) (a) #79223
12/09/01 01:10 AM
12/09/01 01:10 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,280
Fullerton, CA USA
Absolutely. Each neut carries the full load.

[This message has been edited by electure (edited 12-09-2001).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,472 Are you busy
190,717 Re: Forum
180,431 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9674 MB (Peak: 1.1059 MB) Zlib enabled. Server Time: 2019-04-20 11:06:00 UTC