ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
High current GFI vs regular GFCI
by gfretwell. 11/16/18 11:12 PM
This anti-theist is priceless!!!
by djk. 11/14/18 07:19 AM
Single phase and what you call it.
by dsk. 11/12/18 11:10 AM
220/230/240V 60Hz Systems
by Albert. 11/07/18 12:48 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 29 guests, and 18 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Class 1 Div 2 Area Classification #78876
11/02/01 10:25 AM
11/02/01 10:25 AM
B
Big Dog  Offline OP
Junior Member
Joined: Nov 2001
Posts: 3
Elkton, Maryland, USA
According to the Code, Table 515.2 (1999) or 515.3 (2002) for Vent - discharging upward, Class 1 Div 1 for area inside of vent piping or opening, Class 1 Div 1 within 3 ft of open end of vent, extending in all directions, and Class 1 Div 2 for area between 3ft and 5 ft of open end of vent, extending in all directions.

I am using an indoor Class 1 Div 2 rated dust collection system which is removing air and vapors from a Class 1 Div 2 rated area The dust collection system has two vents, one that discharges upward within 18 inches of a non-rated area and another that discharges horizontally within 30 inches of the same non-rated area.

If the dust collection system is taking in only air and vapors from a Class 1 Div 2 rated area, it should only be exhausting Class 1 Div 2 air and vapors, therefore I am unsure if Table 515.3 is applicable for this case.

Could the code be interpreted that the area within 3 ft of the open end of vent, extending in all directions, would be Class 1 Div 2? Therefore could I cover the upward discharge and only utilize the horizontal discharge and relocate to within 36 inches of the non-rated area? Would this still be in violation with the Code?

It is not a bulk storage plant. The Class 1 Div 2 rated area is a lab area. In the lab area liquids, chemicals, and solids of Group D will be used and mixed in open containers.

[This message has been edited by Big Dog (edited 11-02-2001).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Class 1 Div 2 Area Classification #78877
11/02/01 10:46 AM
11/02/01 10:46 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Are you working on a bulk storage plant? Article 515 only applies to bulk storage facilities for flamable liquids. Please give us more details on the installation.
Don(resqcapt19)


Don(resqcapt19)
Re: Class 1 Div 2 Area Classification #78878
11/02/01 12:27 PM
11/02/01 12:27 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Don,

It looks like Big Dog may have added some information to the original post.

Bill

Re: Class 1 Div 2 Area Classification #78879
11/02/01 01:37 PM
11/02/01 01:37 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Big Dog,
The code does not address the area of classification except in specific locations. It only tells us how to install the wiring after the classification has been determined. This question should be addressed by the design engineer that did the original lab classification. If there is not an engineer involved, I guess I would have to be very conservative and classify an area larger than that specified in the code section that you cited. I say larger because your vent is powered and the ones in 515 are not. The force of the fan may extend the ignitable concentration a greater distance form the vent opening. Then on the other hand, it may also serve to dilute the air stream so that the vapor concentration is below the lower flammable limit making it a non classified area. There are too many variables to answer this question on a forum.
don(resqcapt19)


Don(resqcapt19)
Re: Class 1 Div 2 Area Classification #78880
11/02/01 11:39 PM
11/02/01 11:39 PM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
Don,

Once many years ago, It was suggested to me by a salesman for products for the NEC 500 series Articles, " If no one ( project engineer or owner) wants to "Classify" a hazardous area and wants the AHJ to make the classifcation, just Classify the area as the most strict possible ".

CYA.

Glenn

[This message has been edited by Glenn (edited 11-02-2001).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
djk 2
Popular Topics(Views)
251,538 Are you busy
188,706 Re: Forum
178,412 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.006s) Memory: 0.9700 MB (Peak: 1.1076 MB) Zlib enabled. Server Time: 2018-11-17 17:23:50 UTC