Generator disconnect #78833
10/27/01 10:31 PM
10/27/01 10:31 PM
L
lousen  Offline OP
Junior Member
Joined: Jul 2001
Posts: 6
Bryn Mawr, Pa. U.S.A.
Does generator supply entering bldg. underground require a disconnect in bldg? Gen. is 80 feet from bldg.Gen. load 200kva at 208v.

2017 / 2014 NEC & Related Books and Study Guides
Re: Generator disconnect #78834
10/28/01 07:20 AM
10/28/01 07:20 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
Hi lousen!~
good Q
445.18 requires a disco for a genny, but does not specify where...
225-32, general rule , requires a disco. ex#1 could be applied.
If i'm reading this right (part 2 of 225) it matters if the genny serves the outbuilding or not.
others may clarify this better than I
[Linked Image]

Re: Generator disconnect #78835
10/28/01 12:11 PM
10/28/01 12:11 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
As a general rule yes. See 225-31. As Sparky stated Ex #1 in 225-32 could be applied but this would have to be acceptable to the AHJ. I don’t believe many would be inclined to accept this.

Re: Generator disconnect #78836
10/28/01 07:33 PM
10/28/01 07:33 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
Lousen,
can you give us more info here? what is the genny used for? etc..
[Linked Image]

Re: Generator disconnect #78837
10/28/01 11:03 PM
10/28/01 11:03 PM
L
lousen  Offline OP
Junior Member
Joined: Jul 2001
Posts: 6
Bryn Mawr, Pa. U.S.A.
Gen.set mentioned before supplys single owner nursing home.If I open main service disconnect in basement in a fire emergency, Gen. set kicks in.which means power is back on. Nearest disconnect is at Gen. set-80 feet away.This installation is completed but not inspected.

Re: Generator disconnect #78838
10/29/01 07:40 AM
10/29/01 07:40 AM
G
Geno  Offline
Member
Joined: Aug 2001
Posts: 16
Syracuse, NY USA
The answer is yes you do need a disconnect within sight. Check out 700.12(B)(6) in the 2002 NEC.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,379 Are you busy
187,310 Re: Forum
176,654 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9743 MB (Peak: 1.1198 MB) Zlib enabled. Server Time: 2018-09-22 22:42:44 UTC