Photo of the Week:
Closet Meters
Meter Closet
1 members (Scott35), 49 guests, and 33 robots.
#78833 10/27/01 10:31 PM
lousen Offline OP
Does generator supply entering bldg. underground require a disconnect in bldg? Gen. is 80 feet from bldg.Gen. load 200kva at 208v.
#78834 10/28/01 07:20 AM
Hi lousen!~
good Q
445.18 requires a disco for a genny, but does not specify where...
225-32, general rule , requires a disco. ex#1 could be applied.
If i'm reading this right (part 2 of 225) it matters if the genny serves the outbuilding or not.
others may clarify this better than I
#78835 10/28/01 12:11 PM
As a general rule yes. See 225-31. As Sparky stated Ex #1 in 225-32 could be applied but this would have to be acceptable to the AHJ. I don’t believe many would be inclined to accept this.
#78836 10/28/01 07:33 PM
Lousen,
can you give us more info here? what is the genny used for? etc..
#78837 10/28/01 11:03 PM
lousen Offline OP
Gen.set mentioned before supplys single owner nursing home.If I open main service disconnect in basement in a fire emergency, Gen. set kicks in.which means power is back on. Nearest disconnect is at Gen. set-80 feet away.This installation is completed but not inspected.
#78838 10/29/01 07:40 AM
The answer is yes you do need a disconnect within sight. Check out 700.12(B)(6) in the 2002 NEC.