Hi lousen!~ good Q 445.18 requires a disco for a genny, but does not specify where... 225-32, general rule , requires a disco. ex#1 could be applied. If i'm reading this right (part 2 of 225) it matters if the genny serves the outbuilding or not. others may clarify this better than I
As a general rule yes. See 225-31. As Sparky stated Ex #1 in 225-32 could be applied but this would have to be acceptable to the AHJ. I don’t believe many would be inclined to accept this.
Gen.set mentioned before supplys single owner nursing home.If I open main service disconnect in basement in a fire emergency, Gen. set kicks in.which means power is back on. Nearest disconnect is at Gen. set-80 feet away.This installation is completed but not inspected.