PVC requirements #78643
10/10/01 12:46 AM
10/10/01 12:46 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
I did a job today and somebody had run PVC on the outside of a home so I replaced it with emt. As far as I know PVC is subject to machanical damage and not legal run along outside walls. I couldn't find it in the code book.


The Golden Rule - "The man with the gold makes the rule"
2017 / 2014 NEC & Related Books and Study Guides
Re: PVC requirements #78644
10/10/01 06:59 AM
10/10/01 06:59 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Article 347 1999 NEC (Art 352, 2002 NEC). Generally speaking, schedule 40 PVC conduit is acceptable outdoors where not subject to physical damage. "Subject to physical damage" is a judgment call. However, schedule 80 PVC is acceptable where subject to physical damage. What did you remove?
BTW,
EMT is not allowed where subject to "severe" physical damage.
My guess is that "severe" alludes to vehicular damage, or industrial environments. [This message has been edited by Redsy (edited 10-10-2001).]

[This message has been edited by Redsy (edited 10-10-2001).]

Re: PVC requirements #78645
10/10/01 11:32 AM
10/10/01 11:32 AM
A
aldav53  Offline OP
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
It was schedule 40 I removed and replaced it with emt, on the back patio of a home, not subject to severe damage, but still needed mechanical protection. PVC also becomes brittle from sun exposure - especially here in Arizona.
Thanks for reply..


The Golden Rule - "The man with the gold makes the rule"
Re: PVC requirements #78646
10/10/01 12:46 PM
10/10/01 12:46 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,904
NY, USA
Al,

To furthur elaborate on Redsy's answer, If you look at Art 347 ('99NEC)(Rigid Nonmetallic Conduit) it starts off (347-1) with a description and characteristics of the conduit and then follows in 347-2 and 347-3 with the uses permitted and not permitted. This same information is in the NEC for each type of conduit, raceway, etc. (348 is for Emt)

As far as what best to use, that would depend on the situation. I'll bet in Arizona you can get some pretty nasty looking pvc sags! Joe T. had a great picture of that somewhere.

Take care,
Bill


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
BigB 3
Popular Topics(Views)
252,734 Are you busy
189,571 Re: Forum
179,240 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 14 (0.004s) Memory: 0.9596 MB (Peak: 1.0903 MB) Zlib enabled. Server Time: 2019-01-18 22:47:26 UTC