ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Nightmare Panels
 Nightmare Panels

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 35 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#78541 10/03/01 11:38 AM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
For some more info on the U.K. IEE Wiring Regs., you might like to look at the following:
http://www.tlc-direct.co.uk/Book/1.1.htm

Horizontal Ad
#78542 10/03/01 08:12 PM
Joined: Oct 2000
Posts: 4,138
Likes: 4
Member
Paul,

Interesting stuff!
I came across the following and like the common sense that it portrays:

[Linked Image from tlc-direct.co.uk]


Bill
#78543 10/03/01 08:38 PM
Joined: Oct 2000
Posts: 5,393
S
Member
Paul,
facinating....AND illistrations to all the threads you've provided. [Linked Image]

#78544 10/04/01 05:01 PM
A
Anonymous
Unregistered
I don't see the sense here because of the direction that the shower opens. If the shower opened toward the door, that would be different.

The light switch could be 0 m from the shower and a person in the shower would not be able to reach it (unless he is hanging from the water pipes).

#78545 10/04/01 05:56 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
I think the 0.6m is just a general requirement that no fittings be within that distance of any part of the shower cubicle.

If the shower opened toward the left here, that switch would have to be much farther away under the general rule that it must not be able to be touched by anyone in a bath or shower. The distance specified for that is 2m (about 6' 6").

The twin socket would be allowed only if this were a shower cubicle in, say, a bedroom. In a bathroom, the only socket outlet allowed is a xfmr-isolated low-power one for an electric shaver.

#78546 10/04/01 07:52 PM
A
Anonymous
Unregistered
>the general rule that it must not be able to be touched by anyone in a bath or shower. The distance specified for that is 2m (about 6' 6").

Anyone who could reach that far would not technically be in the shower. [Linked Image]

#78547 10/04/01 07:58 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
Quote
Originally posted by Dspark:
>
Anyone who could reach that far would not technically be in the shower. [Linked Image]

Precisely their objective!

Strangely though, we can have "instant" electric showers fitted right in the cubicle under the shower head with just a thin layer of plastic cover and some sealant (we hope!) between a cascade of water and 240V to ground. Then they make such a fuss about not having a socket anywhere in a bathroom. Go figure.

Horizontal Ad
#78548 10/04/01 09:33 PM
Joined: Oct 2000
Posts: 4,138
Likes: 4
Member
The point I was trying to make was that we have no such distance requirements (in the NEC) for switches or receptacles from a shower or bathtub. It is something that I cannot understand.


Bill
#78549 10/04/01 10:03 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
The "old thread reviver" is at it again...
Check this out Paul, an interesting thread...

[Linked Image]

Go here for more!


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#78550 10/04/01 10:47 PM
A
Anonymous
Unregistered
>Precisely their objective!
But the objective can be met with just 1 m of separation (30" NEC) unless you have some really tall people in which case, they are probably at greater risk for taking out luminaires with their heads.

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
BigB 7
Jam85 3
Popular Topics(Views)
329,178 Are you busy
254,113 Re: Forum
236,551 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5