10 foot tap rule #78519 10/01/01 11:18 AM
Joined: Oct 2001
Posts: 2
N
NBuc100101@peoplepc.com Offline OP
Junior Member
We have a main breaker in an electrical enclosure (300 A). We come off of the top of the breaker to a 30 A breaker in the same enclosure. This is within ten feet. Can we go to field devices outside the enclosure off of the load side of the 30 A breaker?

2017 / 2014 NEC & Related Books and Study Guides
Re: 10 foot tap rule #78520 10/01/01 01:20 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
You can go anywhere you want off the load side of the 30 amp breaker as long as you use 30 amp wire. If by "come off the top of the breaker", you mean that you have landed the tap wires in the same terminal as the feeder conductors, you have a violation unless the terminals are listed for those two conductors.
Don(resqcapt19)


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,731 Are you busy
204,964 Re: Forum
193,077 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3