ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Closet Meters
Meter Closet

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 36 guests, and 26 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
A
Anonymous
Unregistered
I will be running three new circuits to a kitchen. Two will serve two double duplex above countertopo outlets each with a GFCI outlet, and the third will be to a simplex outlet to power just the refrigerator. Can I safely and properly run one neutral for these three circuits?

I will also be running a new circuit to the bathroom with one GFCI duplex outlet on it. Can I safely and properly use that same neutral above? =TB=

Horizontal Ad
A
Anonymous
Unregistered
>Can I safely and properly run one neutral for these three circuits?
No way! A "neutral" is a current-carrying grounded conductor.

>Can I safely and properly use that same neutral above?
No. And frankly, this question shows that you know enough to be very dangerous.
I strongly caution you against doing whatever you have planned... especially as it pertains to taking senseless shortcuts.

You have scared me.

Joined: Oct 2000
Posts: 5,393
S
Member
Dennis,
you don't suppose Tom has 3 ph ???

Joined: Jun 2001
Posts: 642
N
Member
No way any one should even consider doing what tom is thinking about. Even with 3 phase.


ed
Joined: Oct 2000
Posts: 2,725
Likes: 1
Broom Pusher and
Member
Mr. Brooklyn,

The reason everyone is so upset is because the common neutral conductor will be overloaded, and that's not good!

Running the circuits as you have described them will result in as much as 40 amps flowing in the common neutral during peak usage. If they were all on the same Line [AKA "Phase"], that would result in as much as 80 amp load on the common neutral during peak use. That would fry a #12 cu conductor, which is good for only about 30 amps max [fused or breaker size is 20 amps max in most conditions].

What you should do in your case is to run a 3 wire circuit for the Kitchen appliance circuits, place the "Hots" on opposite "Phases" [so that if you checked the voltage between the two hots, there will be 240 volts]. If you do not read 240 volts across the two hots, or if you read no voltage, chances are they are not on opposite lines. Using a two pole circuit breaker could assist in this goal [full space 2 pole units, not just simply a "Stacked" 1 pole breaker]. The type of panel used will determine the exact arrangement. If this is not possible, use two separate 12-2 NM cables - one per 4 plex receptacle / circuit.

For the other two circuits [the refrigerator and the bathroom circuits], use separate 2 wire runs for those circuits. One 12-2 NM cable for the refrigerator circuit, one 12-2 NM cable for the bathroom circuit.

As with the others, I also suggest that you seek the assistance of a Qualified Electrical Installer for this installation. The results of wiring the installation the way you first planned would easily result in a fire!!!
This is not an insult, rather it's a very helpful and serious suggestion!

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Oct 2000
Posts: 2,749
Member
Scott:

Good Advice! I would like to add the following:

NM Cables are required to be identified as NM-B to comply with rules in Section 110-3(b) and Article 336.

I know that's what you meant, but if the installer used Type NM (pre 1984 cable) it would be a violation.


Joe Tedesco, NEC Consultant
Joined: Oct 2000
Posts: 5,393
S
Member
are we in a 'dwelling' using NM-B ??

Horizontal Ad
Joined: Dec 2000
Posts: 4,294
Member
Mr. Brooklyn,
I don't recommend your doing what I suggest here, I'm just throwing it in to see the other guy's thoughts, as I've wondered. I haven't and wouldn't do this myself.

What if the run was in conduit, properly phased, and had a #8 neut? (Is that compliant?)

A
Anonymous
Unregistered
Hi Guys:
Thanks for the concerned replies. I see that I raised some eyebrows to say the least on this one; it looks like I better re-read my Wiring 1-2-3 book. I'll do as Scott35 said using a 2 pole breaker on the two kitchen circuit and use seperate 12-2s on the two others. I would be using the common type of BX, I'm not sure what NM-B is. My house is from 1907 and I generally, but not in all cases, have been replacing the old cloth covered wire cable as I renovate from room to room.

Joined: Aug 2001
Posts: 7,520
P
Member
I'm not sure what your NEC says about it, but in the U.K. our "code" specifies that each individual branch circuit leaving a distribution panel must have its own neutral.
One large neutral to two or three branches might be OK from the ampacity point of view, but if someone shut off one breaker to work on an outlet they could unwittingly break into a neutral - believed dead - which is still carrying current on the other circuits. Not good.

Joe: NM is Romex, right? What exactly is the difference between NM and NM-B?


[This message has been edited by pauluk (edited 09-26-2001).]

Page 1 of 4 1 2 3 4

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
akmaster
akmaster
alaska
Posts: 75
Joined: June 2012
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
329,934 Are you busy
254,767 Re: Forum
237,185 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5