Member
Installing outlets in a parking garage. Is there a standard for this as to the location. These will be wall mounted and will be used for maintenance purposes within a secured area. Also do they need to be GFI, currently plan to install all on one circuit NEMA 1.
Need comments.
thanks

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Nov 2000
Posts: 2,148
R
Member
Robert,
Vehicle maintenance or building maintenance?
Don(resqcapt19)


Don(resqcapt19)
Joined: Feb 2001
Posts: 62
M
Member
Test. Had problems with my computer!

[This message has been edited by Mike (edited 09-06-2001).]

Joined: Aug 2001
Posts: 10
R
Robert Offline OP
Member
Quote
Originally posted by resqcapt19:
Robert,
Vehicle maintenance or building maintenance?
Don(resqcapt19)

Vehicle maintenance. If the spec states that the outlets be GFI with weatherproof covers within public spaces, and this is considered secured (police vehicles only), then is there an arguement for that this is "not a public space"?

Joined: Nov 2000
Posts: 2,148
R
Member
Robert,
That will have to be an Article 511 installation. 511-10 requires GFCI protection for any receptacles that will be used for portable repair and diagonstic equipment. You will also have to deal with Class 1 Division 2 locations, maybe even Division 1 if there is a pit. If it is a wet location then weatherproof covers will be required. The specs for the job may exceed the NEC requirements and must be complied with per the contract. They are not enforcable by the electrical inspector, but are enforcable in civil court.
Don(resqcapt19)


Don(resqcapt19)
Joined: Aug 2001
Posts: 10
R
Robert Offline OP
Member
thanks, I had been arguing that we needed however, kept receiving response that since it was considered "secured" and not "public", we did not need to comply.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Jim M 5
Trumpy 4
Popular Topics(Views)
297,362 Are you busy
228,239 Re: Forum
213,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5