Joined: Aug 2001
Posts: 3
OP
Junior Member
|
I just purchased a new Kenmore oven and the manual calls for a minimum of 8 Gauge solid copper on a 40 Amp circuit. I went to Home Depot and purchased 60 ft. of 8-3 with ground. When I got home I noticed that it is NOT solid copper but stranded copper. Will this matter? the manual specifically calls for solid. should I worry about it or is it ok since it will be on a 40 Amp breaker?
Just bought the place and don't want to burn it down! (wife would be angry) Thanks.
|
|
|
|
Anonymous
Unregistered
|
You probably should have gotten 60' of 6-3-G (because of distance if your wife cooks much). Stranded wire is fine. Solid copper is more difficult to work with.
[This message has been edited by Dspark (edited 08-21-2001).]
|
|
|
|
Anonymous
Unregistered
|
Your wire is solid copper in the sense that it is not copper-clad aluminum or pure aluminum either of which would require a heavier gage.
|
|
|
|
Joined: Oct 2000
Posts: 4,145 Likes: 4
Member
|
Todd, It sounds like you are unfamiliar with this situation and would no doubt be better off with some help in this. I would suggest that you contact someone locally that is Licensed/Certified and capable of handling this. Everyone will sleep better at night. Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
I would ask Kenmore if that could be a typo
|
|
|
|
Anonymous
Unregistered
|
I think it just means pure copper rather than aluminum, steel, carbon, or anything else.
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
Probably; I'm not aware of any 8-3 solid in a cable
|
|
|
|
Anonymous
Unregistered
|
8-3-G solid copper is not something I would want to have to unroll much less bend.
|
|
|
|
Joined: Aug 2001
Posts: 545
Member
|
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Aug 2001
Posts: 3
OP
Junior Member
|
Hmm... back to Home Depot I go! Good thing you can return cut wire there...
I didn't take distance into consideration when I read the owner's manual. Now that I think about it I know 6 will be a better choice. I am installing this into an 1950 house and the gap between the plaster and cinder block is only about an inch so I was worried about the wire being to big to install. I am going to install this in conduit because of this.
Although 8 on a 40 would have been safe... I don't want to be tripping breakers while trying to cook dinner.
Thanks for everyones advice!
|
|
|