J-box grounding #78064
08/13/01 04:31 PM
08/13/01 04:31 PM
T
tmon  Offline OP
Member
Joined: Jul 2001
Posts: 29
I would like to know everyones opinion on the grounding of every switch, receptacle and junction box. Are you guys requiring and/or installing a grounding jumper from the equipment grounds to the box?

2017 / 2014 NEC & Related Books and Study Guides
Re: J-box grounding #78065
08/13/01 05:55 PM
08/13/01 05:55 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
My opinion tmon, is not necessarily code driven as much as liability driven.

I say ground it ALL, a small price to pay for some sound sleep.

Of interest, i believe 380-12 addressed more stingent grounding of switches in the 99' code cycle.

[Linked Image]

Re: J-box grounding #78066
08/13/01 06:51 PM
08/13/01 06:51 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Could you be more specific?
As far as j-boxes, I dont believe you have a choice if an EGC is run.(See 250-148)
Receptacles, the only other option is self-grounding receptacles.
As far as switches, see 380-9(b)

Re: J-box grounding #78067
08/13/01 08:17 PM
08/13/01 08:17 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
Ground it, Ground it, Ground it.

Re: J-box grounding #78068
08/19/01 08:15 AM
08/19/01 08:15 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
250-148 (a) Says If you have a separate grounding conductor pulled in the box, it will be bonded to that box. Nuff said ?

Re: J-box grounding #78069
08/19/01 08:20 AM
08/19/01 08:20 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Shoot !!! another half answer, lemme do some more 'splainin' . Our specs at Dulles airport require that 1) You WILL pull an equipment grounding conductor, and 2) You WILL land it to any box it goes through - which, of course is very plain. Why ? you may ask.

In these days of cell phones, FRS radios, etc.. we find that RF has a nasty way of getting into and interfering with intricate systems. Also,Bill Summers stated several years ago that he wanted to see the practice of conduit bonding ended, then went into an expanation that convinced me thoroughly. There is the code, and a very quick reason.

Re: J-box grounding #78070
08/21/01 04:56 PM
08/21/01 04:56 PM
G
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
To the doubter's, I suggest looking at the 1995 Annual Meeting NATIONAL ELECTRICAL CODE REPORT on PROPOSALS ( ROP );

Log # 950
5 - 309 - (250-114 )

on page 249.

Glenn


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,121 Are you busy
189,133 Re: Forum
178,803 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.004s) Memory: 0.9857 MB (Peak: 1.1381 MB) Zlib enabled. Server Time: 2018-12-10 06:47:56 UTC