J-box grounding #78064 08/13/01 05:31 PM
Joined: Jul 2001
Posts: 29
T
tmon Offline OP
Member
I would like to know everyones opinion on the grounding of every switch, receptacle and junction box. Are you guys requiring and/or installing a grounding jumper from the equipment grounds to the box?

2017 / 2014 NEC & Related Books and Study Guides
Re: J-box grounding #78065 08/13/01 06:55 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
My opinion tmon, is not necessarily code driven as much as liability driven.

I say ground it ALL, a small price to pay for some sound sleep.

Of interest, i believe 380-12 addressed more stingent grounding of switches in the 99' code cycle.

[Linked Image]

Re: J-box grounding #78066 08/13/01 07:51 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Could you be more specific?
As far as j-boxes, I dont believe you have a choice if an EGC is run.(See 250-148)
Receptacles, the only other option is self-grounding receptacles.
As far as switches, see 380-9(b)

Re: J-box grounding #78067 08/13/01 09:17 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
Ground it, Ground it, Ground it.

Re: J-box grounding #78068 08/19/01 09:15 AM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
250-148 (a) Says If you have a separate grounding conductor pulled in the box, it will be bonded to that box. Nuff said ?

Re: J-box grounding #78069 08/19/01 09:20 AM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
Shoot !!! another half answer, lemme do some more 'splainin' . Our specs at Dulles airport require that 1) You WILL pull an equipment grounding conductor, and 2) You WILL land it to any box it goes through - which, of course is very plain. Why ? you may ask.

In these days of cell phones, FRS radios, etc.. we find that RF has a nasty way of getting into and interfering with intricate systems. Also,Bill Summers stated several years ago that he wanted to see the practice of conduit bonding ended, then went into an expanation that convinced me thoroughly. There is the code, and a very quick reason.

Re: J-box grounding #78070 08/21/01 05:56 PM
Joined: Jan 2001
Posts: 75
G
Glenn Offline
Member
To the doubter's, I suggest looking at the 1995 Annual Meeting NATIONAL ELECTRICAL CODE REPORT on PROPOSALS ( ROP );

Log # 950
5 - 309 - (250-114 )

on page 249.

Glenn


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,026 Are you busy
205,035 Re: Forum
193,143 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3