Well they did it to me...
I found out today... with 9 days and counting to finish... that the show lighting will require 240V 200A... not sure how they will be split up... 10 20A 240V circuits?... Don't know yet....
The service I'm working on tomorrow for it only has a 25KVa Xformer. There is a 50KVa about 500 feet away...
It is going to be a miracle if I pull this off.
The sound wants 6 20A circuits that does not share the pole(s) with any other non-sound circuit. So figure 100A at 120V for them (80% of 20A x 6= 96A)
This doesn't include any ambient/security/convenience lighting or any of the concessions.
The show has been moved to a new location since the last time I mentioned the festival...
My questions are many...
Is SOW cable my only option? ($$$$$$$$$)
Can I run Schedule 80 PVC on the surface of the ground? (with THWN) How do I secure it?
What other options do I have for exposed wet location cable? UF? (Subject to probable physical damage)
This will be a Temporary Wiring situation, under NEC Chapters 305 and 525.
I have 9 days.... It wasn't my fault...
But this whole $50,000 investment is riding on my shoulders to produce a miracle. And they're giving me a whopping $700 to start with tomorrow.
(Plus I'm roughing in a house for a GC I want to impress!)
How much headroom do I have with a 25KVa Xformer? 108A @ 240V?
Boy... if the lighting was 120V for 200A I'd be set...
Gaffer's nightmare? (Did I get the name right this time?)
Plus my band plays a 1-1/2 hour set on Friday night there...