Additional box volume? #77932 07/22/01 10:47 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
When using a 1/2" deep pancake box, with a volume of 8", this volume is considered with a cover on the box, correct? If using one to install a ceiling fan, or any other fixture that does not have a plate that sits right on the fixture, is additional volume provided by the fixture?
I dont' think 370-16(a) applies because fixtures are not marked with volumes, but I'm also looking at 410-10.

2017 / 2014 NEC & Related Books and Study Guides
Re: Additional box volume? #77933 07/22/01 11:39 AM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
Wow...

Yes, I was under the assumption that one could count the escutcheon (canopy) as part of the wire fill area, but 370-16(a) clearly states "...that are marked with their volume in cubic inches..." Could this mean that even if they marked the volume, but used the metric system (which the code uses at times and will next year) then it cannot be used?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Additional box volume? #77934 07/22/01 03:25 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Redsy,
good one. my code book is dogeared from Q's like this! Once again,years of assumption falls flat on it's face.... There must be some recourse for the lowly pancake box???

[Linked Image]

Re: Additional box volume? #77935 07/22/01 08:55 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
Virgil's found yet another hole in the wording of the Code! It's looking more and more like Swiss Cheese. Given 3 years to think & discuss, you'd think the CMP's would fill more of the gaps!

Re: Additional box volume? #77936 07/23/01 01:43 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Just my opinion,

I think that you can't technically count the canopy space when figuring the box fill for your conductors. The canopy does however absorb the fixture wires (they're already there, right?) so that they do not have to be added into the box fill.
sound reasonable? [Linked Image]

Bill


Bill

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,432
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,017 Are you busy
205,012 Re: Forum
193,127 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3