ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
sec cable code conflict
by gfretwell. 11/17/18 02:19 PM
This anti-theist is priceless!!!
by Texas_Ranger. 11/17/18 02:15 PM
High current GFI vs regular GFCI
by Texas_Ranger. 11/17/18 02:07 PM
Single phase and what you call it.
by dsk. 11/12/18 11:10 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
2 registered members (gfretwell, Texas_Ranger), 31 guests, and 27 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Additional box volume? #77932
07/22/01 09:47 AM
07/22/01 09:47 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
When using a 1/2" deep pancake box, with a volume of 8", this volume is considered with a cover on the box, correct? If using one to install a ceiling fan, or any other fixture that does not have a plate that sits right on the fixture, is additional volume provided by the fixture?
I dont' think 370-16(a) applies because fixtures are not marked with volumes, but I'm also looking at 410-10.

2017 / 2014 NEC & Related Books and Study Guides
Re: Additional box volume? #77933
07/22/01 10:39 AM
07/22/01 10:39 AM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Wow...

Yes, I was under the assumption that one could count the escutcheon (canopy) as part of the wire fill area, but 370-16(a) clearly states "...that are marked with their volume in cubic inches..." Could this mean that even if they marked the volume, but used the metric system (which the code uses at times and will next year) then it cannot be used?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Additional box volume? #77934
07/22/01 02:25 PM
07/22/01 02:25 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
Redsy,
good one. my code book is dogeared from Q's like this! Once again,years of assumption falls flat on it's face.... There must be some recourse for the lowly pancake box???

[Linked Image]

Re: Additional box volume? #77935
07/22/01 07:55 PM
07/22/01 07:55 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,276
Fullerton, CA USA
Virgil's found yet another hole in the wording of the Code! It's looking more and more like Swiss Cheese. Given 3 years to think & discuss, you'd think the CMP's would fill more of the gaps!

Re: Additional box volume? #77936
07/23/01 12:43 AM
07/23/01 12:43 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Just my opinion,

I think that you can't technically count the canopy space when figuring the box fill for your conductors. The canopy does however absorb the fixture wires (they're already there, right?) so that they do not have to be added into the box fill.
sound reasonable? [Linked Image]

Bill


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
KevinL 2
Popular Topics(Views)
251,541 Are you busy
188,707 Re: Forum
178,412 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9692 MB (Peak: 1.1101 MB) Zlib enabled. Server Time: 2018-11-17 19:29:44 UTC