#77932 07/22/01 09:47 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
When using a 1/2" deep pancake box, with a volume of 8", this volume is considered with a cover on the box, correct? If using one to install a ceiling fan, or any other fixture that does not have a plate that sits right on the fixture, is additional volume provided by the fixture?
I dont' think 370-16(a) applies because fixtures are not marked with volumes, but I'm also looking at 410-10.

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#77933 07/22/01 10:39 AM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Wow...

Yes, I was under the assumption that one could count the escutcheon (canopy) as part of the wire fill area, but 370-16(a) clearly states "...that are marked with their volume in cubic inches..." Could this mean that even if they marked the volume, but used the metric system (which the code uses at times and will next year) then it cannot be used?


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#77934 07/22/01 02:25 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Redsy,
good one. my code book is dogeared from Q's like this! Once again,years of assumption falls flat on it's face.... There must be some recourse for the lowly pancake box???

[Linked Image]

#77935 07/22/01 07:55 PM
Joined: Dec 2000
Posts: 4,291
Member
Virgil's found yet another hole in the wording of the Code! It's looking more and more like Swiss Cheese. Given 3 years to think & discuss, you'd think the CMP's would fill more of the gaps!

#77936 07/23/01 12:43 AM
Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
Just my opinion,

I think that you can't technically count the canopy space when figuring the box fill for your conductors. The canopy does however absorb the fixture wires (they're already there, right?) so that they do not have to be added into the box fill.
sound reasonable? [Linked Image]

Bill


Bill

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles
Posts: 349
Joined: April 2004
Top Posters(30 Days)
BigB 4
triple 3
Popular Topics(Views)
303,012 Are you busy
232,123 Re: Forum
216,775 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5