Commerical Kitchen #7766
02/20/02 06:43 PM
02/20/02 06:43 PM
B
Boomer  Offline OP
Junior Member
Joined: Feb 2002
Posts: 5
In a commerical kitchen when the fire suppression system in the range hood senses a fire and shuts off the gas valves, by the NEC should it also shut the power off to ranges & ovens under the hood? Boomer

Work Gear for Electricians and the Trades
Re: Commerical Kitchen #7767
02/20/02 09:16 PM
02/20/02 09:16 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Boomer,
It’s not an NEC requirement. I believe it is in the fire codes. Generally all power under the hood must shut down. Make up air must shut down and exhaust fans must turn on or continue to operate. Check with the local AHJ in your area as requirements vary from place to place.

Re: Commerical Kitchen #7768
02/21/02 09:59 AM
02/21/02 09:59 AM
B
Bob Hinshaw  Offline
Junior Member
Joined: Jan 2001
Posts: 5
Tipp City, Ohio, USA
Boomer,
A shunt trip circuit breaker should be installed through the fire panel at the hood.
All lights and especially the exhaust fans should be wired into them. When the fire systems is activated, it will shut power off to the range hood. There should be a wiring diagram in the fire panel for the proper wire connections.

Re: Commerical Kitchen #7769
02/21/02 06:00 PM
02/21/02 06:00 PM
M
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
I believe that NFPA allows exhaust fans to continue to run but any make up air must be shut down.

And I think this is a pretty new rule, maybe 95?

Re: Commerical Kitchen #7770
02/23/02 10:07 AM
02/23/02 10:07 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Although a shunt-trip breaker is an acceptable method, the circuits can be run through electrically held contactors controlled by the fire panel. The benefits are that you don't have to lose the extra breaker space required by the shunt c/b, no external power is required to operate the shunt in the event of the shunt's control circuit being turned off (which could go undetected), and $$$.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 9
Popular Topics(Views)
249,439 Are you busy
187,355 Re: Forum
176,696 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.005s) Memory: 0.9670 MB (Peak: 1.1049 MB) Zlib enabled. Server Time: 2018-09-25 01:17:15 UTC