Is a 120 volt 20 amp duplex receptacle required to be GFCI protected? It will be used for a coffee maker at a Fair.
Frank (cinkerf)
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
525-18(c) would have 305-6(b)(2) applied, but this is debatable given the code loop there.
|
|
|
|
Joined: Oct 2000
Posts: 4,149 Likes: 4
Member
|
Frank,
Code aside, I would say to be on the safe side it should. How can anyone tell what a duplex receptacle would really be used for? Unless for some reason the coffeemaker is incompatible with the GFCI. Just my opinion.
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
Bill; agreed,obvious,no arguement...
bear with me as i entertain the inspectors wish for NEC validation...
525-13(a) states it's compliance with chap 1-4, so would location becomes an issue ?
210-8 could read a GFI into or out of this.
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
My take on article 525 is that it only requires GFI protection for portable wiring & equipment (525-3). I realize the coffee pot is portable, but if the receptacle is part of a fixed wiring sytem, it probably doesn't need to be GFI protected.
GFI receptacles are cheap, if nuisance tripping isn't going to be a problem, I would go ahead & use it.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
how about 215-9 , i would think this would be a bid winner...
|
|
|
|
Anonymous
Unregistered
|
My question would be: Is the coffee maker close to a sink (within 6 feet). If so, then yes, you would need to protect your 20 amp receptacle. It doesn't matter if it's a duplex. Any receptacle within 6 feet of a sinks edge should be gfci protected. Also, I would have it protected if it's exposed to weather--outside rain, or etc. Originally posted by cinkerf: Is a 120 volt 20 amp duplex receptacle required to be GFCI protected? It will be used for a coffee maker at a Fair.