What are some of the approved uses for standard Extension cords?

Bill


Bill
Horizontal Ad
Joined: Oct 2000
Posts: 5,393
S
Member
my 2 cnts;
for nothing permanent


[Linked Image]

Joined: Mar 2001
Posts: 2,056
R
Member
When you say standard, do you mean not heavy duty, or hard & extra hard usage? We use them as power cords for starters on portable pumps in a Hazardous Location. Seals are required. I have also used them for temporary power on test bin agitator motors to conduct mixing studies in our research facility. Removed after the test, of course?

[This message has been edited by Redsy (edited 05-21-2001).]

Joined: Oct 2000
Posts: 4,140
Likes: 4
Member
Redsy,

By standard, I mean that they are not made for a specific purpose. Or have inline GFCI protection.
I'm under the impression that the cords We use for our work are supposed to have GFCI protection somewhere, either in the circuit or inline.

What can you legally use the little lamp cord (zipcord) extensions for?

[Linked Image]
Bill


Bill
Joined: Oct 2000
Posts: 5,393
S
Member
what is 210-50(b)telling us to do?
does 400-7 apply to zip cord ( i don't see it in the table)

[Linked Image]

Joined: Nov 2000
Posts: 123
D
doc Offline
Member
well do not know about code wise but i can remember grand ma whooping on me with one when i did something wrong seems she had those darn things everywhere


MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Yeah... my Mom's favorite was the percorlator cord... I wonder if there is something freudian going on here... We became electricians in the basic need to "control the wire"...

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Horizontal Ad
Joined: Oct 2000
Posts: 4,140
Likes: 4
Member
Whoa,

You guys are gettin deep!

[Linked Image]
Bill


Bill
Joined: May 2001
Posts: 176
W
Member
If the question refers to "flexible cords and cables", then Art. 400 would be the controlling NEC rules. Specifically, Art. 400-7 Uses permitted and 400-8 Uses Not Permitted. "Standard" extension cords are used in our homes to "extend" the receptacle power to a more convenient location for power usage, and on construction sites for the same reason. However, all are supposed to be temporary as sparky says "nothing permanent".

Joined: Oct 2000
Posts: 5,393
S
Member
WARREN1
true, but then it get's to again be somewhat definitional as to what would be considered permanent.

granny could unplug them once in a while
[Linked Image]
there are always loopholes....

as to Bill's original Q, i would further add.....
"does the NEC address extention cord use?"

305 & 400 aside.

[Linked Image]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,443
Joined: July 2002
Top Posters(30 Days)
BigB 6
timmp 2
Popular Topics(Views)
329,661 Are you busy
254,498 Re: Forum
237,002 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5