ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
"Esoteric" countries and their wiring practices?
by Texas_Ranger. 04/20/19 07:00 PM
Norwegian power?
by Texas_Ranger. 04/20/19 06:27 PM
Welded Copper Connections
by gfretwell. 04/19/19 04:46 PM
Israel
by annemarie1. 04/18/19 02:35 PM
Water heater calculationsSo when I count calculati
by watersparkfalls. 04/13/19 12:43 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 6 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Cable Trays #77271
05/19/01 08:23 AM
05/19/01 08:23 AM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
given a 24" cable tray that contains only 500mcm stacked in layers what is the violation there?

twelve 500mcm cables are distributed across the bottom of the tray...ladder type...on top of those is another layer.

as i read the code it doesnt allow for this.

given the addition of multi-conductor cables it gets even more restrictive.

thanks for any input

2017 / 2014 NEC & Related Books and Study Guides
Re: Cable Trays #77272
05/19/01 09:24 PM
05/19/01 09:24 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
OK Frodo,
I'm bored and no one else has answered, I'll bite.

318-10(1) seems clear with no provisions for exceptions.

Single conductor cables, 2000v or less,

(1) Where all cables are 1000kcmil or larger, the sum of the diameters shall not exceed the cable tray width.

GJ

Re: Cable Trays #77273
05/19/01 09:29 PM
05/19/01 09:29 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
If the voltage is over 2kv, (this is a powerhouse, right?)
then 318-12 and 318-13 are even more restrictive.

Re: Cable Trays #77274
05/19/01 09:32 PM
05/19/01 09:32 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
It's Saturday night and I'm digging thru the NEC and posting at ECN........

man, I gotta' get a life. [Linked Image] [Linked Image] [Linked Image]

Re: Cable Trays #77275
05/19/01 10:31 PM
05/19/01 10:31 PM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
Quote
Originally posted by golf junkie:
It's Saturday night and I'm digging thru the NEC and posting at ECN........

man, I gotta' get a life. [Linked Image] [Linked Image] [Linked Image]


yeah its sat night and being away from home is about as bad...

yes it is a powerhouse...but the voltage is 480vac...

the contractor is not even attempting to follow the nec on the job...

there are a lot of violations around....this is one that i really wanted to be sure on so i figured i would ask for some opinions..they have stacked a couple layers of 500MCM conductors in a 24" tray and i think they are planning on dumping some control cables in there as well as some multi-conductor power cables...3/C 12, etc...

ge requires that the nec be followed if it is on our equipment even if it is a powerhouse...i have never seen a job where the nec was not recognized..

pictures available

thanks for the input

Re: Cable Trays #77276
05/19/01 11:10 PM
05/19/01 11:10 PM
F
frodo  Offline OP
Member
Joined: May 2001
Posts: 129
louisville, ky usa
Quote
Originally posted by golf junkie:
OK Frodo,
I'm bored and no one else has answered, I'll bite.

318-10(1) seems clear with no provisions for exceptions.

Single conductor cables, 2000v or less,

(1) Where all cables are 1000kcmil or larger, the sum of the diameters shall not exceed the cable tray width.

GJ


don't you mean 318-10 (2) 500mcm are smaller than 1000kcmil i thought?

i was thinking 318-8, 9 & 10 covered it pretty well, indicating that you can not stack single conductors except for grouping?

Re: Cable Trays #77277
05/19/01 11:35 PM
05/19/01 11:35 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
Frodo,
You're right....
I had confused the conductor size with your post on seal offs.

My bad.

GJ


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,524 Are you busy
190,766 Re: Forum
180,487 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.005s) Memory: 0.9850 MB (Peak: 1.1376 MB) Zlib enabled. Server Time: 2019-04-22 10:41:07 UTC