can you install a 2" conduit in front of and to the left looking at the front of the panelboard (600VAC)?

as i read section 110-26 (2), (3) it appears that it would be a violation if the right edge of the conduit is lined up directly with the left side of the panelboard cover looking at it from the front. i have photos available as well.

the conduit is around 6" in front and to the left side of the panelboard....

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2001
Posts: 507
G
Member
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.

Hope that makes sense, if not ask again.

GJ

Joined: May 2001
Posts: 129
F
frodo Offline OP
Member
Quote
Originally posted by golf junkie:
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.

Hope that makes sense, if not ask again.

GJ

thanks,
i have a contractor that i am supervising and they have installed a 2" conduit so close to the rule it is questionable in my mind. as i read in 110-26 (3) i must consider (e) as well, in addition to the 6" maximum beyond the front of the equipment...

thank you for taking the time to reply...

regards

frodo

Joined: Oct 2000
Posts: 5,392
S
Member
frodo;
i'm farily sure 110-26 (3) was made for troughs, but is ok for any pipework associated with the panel.

make sure your panel door can open 90 deg.----110-26-(2) with that pipe...