sparky Offline OP
I have noticed different methods for terminating stranded wire to devices.
as not all devices are created equal,the method varies...
what i see most of is stranded made to devices that are meant for solid only without forks.
the wire is stripped, a small 1/8" piece of insulation is used to hold the very end from fraying, and the whole deal is placed under a device screw.
comments???
The UL White book receptacle section (RTRT) says: "Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded building wires.
don(resqcapt19)
[This message has been edited by resqcapt19 (edited 05-15-2001).]
comments???
I do this too. I don't really like it; the more you tighten the screw, the more the wire seems to get pushed out from under the head of the screw. But I don't know of any better way.
I've done that to in a pinch..
Ideal makes these forked terminals that are on the end of a little blue wire nut. They're much cheaper than crimp type, easier to use and look a lot better too. I use them if space permits, otherwise I use the ol' trick Steve mentioned.
[This message has been edited by sparky66wv (edited 05-15-2001).]
-Virgil
5 Star Inspections
Member IAEI
If you twist the strands counterclockwise first, tightening the screw will further twist them instead of untwisting them.
Anonymous
Unregistered
I think that's if you are are inserting from the left side.
sparky Offline OP
Thanks... [Linked Image]
always good info from you guys!
Or in the southern hemisphere!
But seriosly, it works
Where have I gone wrong?
I was always told to have the wire inserted with the turn of the thread ( clockwise ) and that would eliminate the insert from 'right side' comment.
Of course if the binding screw is 'counter clockwise thread' that would be a different story.
Glenn
