a brain drain... #77138 05/05/01 06:41 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline OP
Member
230-53
"raceways enclosing service entrance conductors shall be raintight and arranged to drain"

drain what, if it's raintight?

does anyone know of a listed drain for this?

[Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: a brain drain... #77139 05/05/01 09:50 PM
Joined: Apr 2001
Posts: 507
G
golf junkie Offline
Member
The local interpretation on this has always been that you cannot arrange the raceway so that it becomes a plumbing trap.

This is just good general practice for all raceways exposed to weather.....not just the service entrance.

I'm sure we have all pulled apart conduit that is full of water in spite of the fact that it is properly installed, (according to the NEC). I know I have many, many, times

Re: a brain drain... #77140 05/07/01 09:50 PM
Joined: Apr 2001
Posts: 54
W
wayne Offline
Member
Sparky,
Golfjunkie is right. Art 230-53 is a binary sentence. Raintight and arrange to drain.

Thats when we call in a plumber to help us.
[Linked Image]
Wayne

Re: a brain drain... #77141 05/08/01 07:29 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Along the same lines-Isn't the interior of a raceway which is installed in a wet location considered a wet location? If so the commonly observed practice of installing NM cable in an out door raceway for various reasons( AC whip, to get from an attic to a basement, etc.) is a violation, correct?

Re: a brain drain... #77142 05/08/01 08:20 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
If you look at a 3R enclosure you will find drain holes in the bottom. As far as drains go, there are a number of them available for classified areas and a few for non-classified areas. Stahl makes a plastic drain for threaded conduit systems, but I have not been able to find it at the supply houses. It comes with the power connect kits for some brands of heat trace.
This doesn't meet code, but I have used conduit plugs with small holes drilled in them for drains and also have cut a small notch in the bottom part of a LB gasket to make a drain. Our conduit couplings are straight thread and not watertight. Any time you have a coupling in threaded conduit on a vertical run in a wet location, water will enter the raceway.
don(resqcapt19)


Don(resqcapt19)
Re: a brain drain... #77143 05/09/01 03:29 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline OP
Member
thanks guys,
it just reads odd, i think i was caught in a one sentence code loop there... [Linked Image]

( like the stooges Curley when he plants one foot and goes in a circle...)

[This message has been edited by sparky (edited 05-09-2001).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
271,000 Are you busy
205,004 Re: Forum
193,122 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3