#77138 05/05/01 05:41 PM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
230-53
"raceways enclosing service entrance conductors shall be raintight and arranged to drain"

drain what, if it's raintight?

does anyone know of a listed drain for this?

[Linked Image]

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#77139 05/05/01 08:50 PM
Joined: Apr 2001
Posts: 507
G
Member
The local interpretation on this has always been that you cannot arrange the raceway so that it becomes a plumbing trap.

This is just good general practice for all raceways exposed to weather.....not just the service entrance.

I'm sure we have all pulled apart conduit that is full of water in spite of the fact that it is properly installed, (according to the NEC). I know I have many, many, times

#77140 05/07/01 08:50 PM
Joined: Apr 2001
Posts: 54
W
Member
Sparky,
Golfjunkie is right. Art 230-53 is a binary sentence. Raintight and arrange to drain.

Thats when we call in a plumber to help us.
[Linked Image]
Wayne

#77141 05/08/01 06:29 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Along the same lines-Isn't the interior of a raceway which is installed in a wet location considered a wet location? If so the commonly observed practice of installing NM cable in an out door raceway for various reasons( AC whip, to get from an attic to a basement, etc.) is a violation, correct?

#77142 05/08/01 07:20 AM
Joined: Nov 2000
Posts: 2,148
R
Member
If you look at a 3R enclosure you will find drain holes in the bottom. As far as drains go, there are a number of them available for classified areas and a few for non-classified areas. Stahl makes a plastic drain for threaded conduit systems, but I have not been able to find it at the supply houses. It comes with the power connect kits for some brands of heat trace.
This doesn't meet code, but I have used conduit plugs with small holes drilled in them for drains and also have cut a small notch in the bottom part of a LB gasket to make a drain. Our conduit couplings are straight thread and not watertight. Any time you have a coupling in threaded conduit on a vertical run in a wet location, water will enter the raceway.
don(resqcapt19)


Don(resqcapt19)
#77143 05/09/01 02:29 PM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
thanks guys,
it just reads odd, i think i was caught in a one sentence code loop there... [Linked Image]

( like the stooges Curley when he plants one foot and goes in a circle...)

[This message has been edited by sparky (edited 05-09-2001).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 28
Joined: June 2004
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,454 Are you busy
231,795 Re: Forum
216,401 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5