I've got a couple of questions regarding Roof and Gutter Cable.


  • Can Roof and Gutter cable be spliced? Some of the cables have gotten cut somehow
  • reading the Safety precautions on one of the origional packages says the following:
    Quote
    GROUND all metal gutters and downspouts to 8 ft. driven ground even if downspout enters porcelain or non-metal drainage pipe


Bill


Bill
2017 / 2014 NEC & Related Books and Study Guides
Re: Roof and Gutter cable #77029 04/14/01 07:52 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Bill,

I can't figure out what good those ground rods are going to do unless they get bonded to the buildings grounding electrode system.

I don't see anything in article 426 that prevents splicing. If the manufacturer makes a splice kit, then a splice would definitely be allowed 426-10

Visit the following for more http://raychem.broaddaylight.com/raychem/TFAQ9.shtm

Tom

[This message has been edited by Tom (edited 04-14-2001).]


Few things are harder to put up with than the annoyance of a good example.
Re: Roof and Gutter cable #77030 04/15/01 10:05 AM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline OP
Member
Tom,

Thanks, I was wondering the same thing about the ground rods. It's mentioned twice on the package.

About the splice kit, These are Wrap-on cables. I can't seem to find any info on them online.

Bill


Bill
Re: Roof and Gutter cable #77031 04/15/01 07:57 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Bill,
I think this is just another example of a munufaturer that has no idea how electricl systems work. Grounding is not required here, but bonding is. As Tom stated a rod will not help any if there is a fault in the heat cable.
Does the wording in 426-3 about installing cord connected snow melting equipment per Article 422 mean that we don't have to provide GFP for the snow melting equipment as required by 426-28?
Don(resqcapt19)


Don(resqcapt19)
Re: Roof and Gutter cable #77032 04/16/01 07:15 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline OP
Member
Tom,

Those Raychem cables look much more sophisticated than the series resistive loop cables We have (Dad's house - He cut some with a hatchet chopping ice on the roof [Linked Image]!!) They can be cut anywhere and I assume that the end just needs to be sealed somehow because the current flows across from wire to wire and is self regulating by temperature. They look like they'll save $$ with that feature instead of being Full on all the time like the old ones. So, Maybe we'll just get some new generation Raychems to replace instead of repairing old ones.

Don,

I agree with your comments, as a side note there's no UL mark on the packaging either.

Also, that's a bit confusing to me why Art 426 would refer to 422 like that.
?? [Linked Image]

Bill


Bill
Re: Roof and Gutter cable #77033 04/17/01 05:08 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Bill,

Be prepared to spend some serious $$$ on the Raychem. I've made a few installations & it is great stuff, but it is not inexpenseive.

Here's another site to try, I can't verify the quaulity, but I've seen it mentioned (favorably) by other electricians.
http://www.easyheat.com/roofgutter/

Good luck

Tom


Few things are harder to put up with than the annoyance of a good example.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
271,000 Are you busy
205,004 Re: Forum
193,122 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3