Welding Cable #76955
04/05/01 02:25 PM
04/05/01 02:25 PM
B
Brian  Offline OP
Junior Member
Joined: Apr 2001
Posts: 1
Anaheim, CA, USA
My question is regarding the use of welding cable in panels. Suppliers list the amperage ratings for welding cable. However, the NEC states very little about the use of welding cable other than with welding equipment.

Welding cable offers a couple of great advantages. First, it is very flexible in tight locations. Second, the ampacity is much higher for smaller gauges in comparison to THHN cable for example.

Is welding cable suitable for short distances as an alternative? I have a situation where it would be extremely helpful to use welding cable and was wondering if anyone have any information on this subject.

2017 / 2014 NEC & Related Books and Study Guides
Re: Welding Cable #76956
04/05/01 03:58 PM
04/05/01 03:58 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,372
i beleive it's already done in some applications requiring flexibility.

is this wire type at all referenced in the NEC? #'s or lettered designation...

Re: Welding Cable #76957
04/05/01 09:16 PM
04/05/01 09:16 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Here's my problem with using them...

Welding cable is generally smaller than other cable, for a given ampacity, which has many advantages. However, the temp rating is based on the entire circuit including terminals and devices. At a given ampacity, the welding cable will be warmer, the insulation may be rated for higher temps, but the teminal and device ratings will still prevent you from being allowed to exceed a certain temperature. At this point you're back at square one using the same size cable.

Also, what voltage is welding cable rated for? Most welders are well below 120V to ground, and the insulation may not have the dielectric strength for 600V at higher temps.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Welding Cable #76958
04/05/01 11:28 PM
04/05/01 11:28 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Much of the welding cable has 600 volt insulation, but it is not listed for use in power circuits. The manufacture's information usually says "only for use as secondary conductors for welding equipment". Type W power cable is of the same construction as welding cable but is listed for power circuits and is covered in Article 400. I have used welding cable for temporary power connections with no problems, but never for permanent connections.
Don(resqcapt19)


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,588 Are you busy
190,795 Re: Forum
180,539 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 14 (0.010s) Memory: 0.9601 MB (Peak: 1.0903 MB) Zlib enabled. Server Time: 2019-04-26 11:58:48 UTC