We came across the following installation:

A 75 kVA 480-120/208Y step down transformer protected on the 480V primary side by a 100A fused disconnect switch feeds two 120/208 panelboards. These are two 42 circuit 225 Amp Main Breaker panels loaded to the gills (and contain mini breakers also) from the secondary of the transformer. The low voltage side current rating of the transformer is 203 Amps. As I interpet the code, with the 100 Amp fused disconnect switch on the primary, secondary protection on the transformer is not required.

There is probably not 450 Amps of connected load on the panels, but could someone please refernce what code sections either allow or disallow this installation.

Thanks in advance

Horizontal Ad
#76688 03/15/01 10:19 AM
Joined: Nov 2000
Posts: 2,148
R
Member
WireStu,
You are correct that the transformer itself does not require overcurrent protection on the secondary side, however the conductors feeding the panels may require overcurrent protection. See 240-21(c)(2).
Also this installation would be in violation of 384-15 if all 42 spaces are filled and some of the spaces have 1/2 space breakers in them.
Don(resqcapt19)


Don(resqcapt19)
#76689 03/15/01 02:50 PM
Joined: Jan 2001
Posts: 75
G
Member
Don,

Doesn't 340-3(f) require secondary OC if it is a 4W system [ 208/120V ]?

Glenn

#76690 03/15/01 03:15 PM
Joined: Jan 2001
Posts: 4
W
WireStu Offline OP
Junior Member
Thanks for the responses. A question I still have is although the transformer puts out 208 amps, can 450 amps worth of potential load be connected to it?

Thanks in advance

Stu

#76691 03/15/01 04:33 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Glenn,
Yes, 240-3(f) requires CONDUCTOR overcurrent protection for 3 phase 4 wire systems, but you go to 240-21(c) to find out how to protect these conductors. There is no requirement to protect the trasformer secondary if the primary OCPD is rated at 125% or less of the primary current. The transformer overcurrent protection requirements are all in 450-3.

Stu,
The 100 amp OCPD on the primary will protect the transformer from the 450 amp connected load. A load calculation need to be done to see what the actual load is. The transformer may be too small.

Don(resqcapt19)


Don(resqcapt19)
#76692 03/15/01 06:35 PM
Joined: Jan 2001
Posts: 75
G
Member
Don,

Poor choice of wording in my previopus reply.

I should have said:

Doesn't 240-3(f) require secondary conductor OC protection if it is a 4W system [ 208/120V ].

And added "240-21(c)".

Glenn


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
340,332 Are you busy
265,725 Re: Forum
246,731 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5