double tapped circuit breaker #76475 02/09/01 08:26 PM
Joined: Feb 2001
Posts: 1
G
georggezaf Offline OP
Junior Member
Can anyone cite the NEC Section(s) that do not allow for termination of two branch circuit wires (hots) on a single circuit. Keep in mind that the load does not exceed the circuit breaker rating.

2017 / 2014 NEC & Related Books and Study Guides
Re: double tapped circuit breaker #76476 02/09/01 08:54 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
There is no NEC article, it's more of a "listing" and "rating" deal.

Re: double tapped circuit breaker #76477 02/09/01 09:10 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Take a look at 110-14(a).

Some circuit breakers, most notably Square D QO in 15, 20 & 30 amps are listed and labeled for 2 conductors per terminal, but they are the only ones that I know of.

Tom


Few things are harder to put up with than the annoyance of a good example.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,731 Are you busy
204,964 Re: Forum
193,075 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3