Dedicated Equipment Space #76039
11/03/00 11:29 AM
11/03/00 11:29 AM
J
James Morier  Offline OP
Junior Member
Joined: Nov 2000
Posts: 1
Albany, NY
I have a new installation where the MC ran hot water heat pipes less than 2 inches away from the side of an electrical panel. The heating line contains an automatic air bleeder valve near the top of the panel. The lines do not enter the dedicated equipment space as defined in 110-26.f. The outlet of the bleeder valve points away from the panel and under normal operation, should not cause a water problem. I can not find anything in the code that prohibits this installation. I would like to have the MC move his lines, but I need back-up from the code. Am I missing something?

2017 / 2014 NEC & Related Books and Study Guides
Re: Dedicated Equipment Space #76040
12/04/00 11:41 AM
12/04/00 11:41 AM
C
cinkerf  Offline
Member
Joined: Dec 2000
Posts: 84
Pittsburgh, Pennsysvania. ...
Quote
Originally posted by James Morier:
I have a new installation where the MC ran hot water heat pipes less than 2 inches away from the side of an electrical panel. The heating line contains an automatic air bleeder valve near the top of the panel. The lines do not enter the dedicated equipment space as defined in 110-26.f. The outlet of the bleeder valve points away from the panel and under normal operation, should not cause a water problem. I can not find anything in the code that prohibits this installation. I would like to have the MC move his lines, but I need back-up from the code. Am I missing something?

Depending upon the width of your panelboard you may be able to use 110.26(a)(2)


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
Popular Topics(Views)
252,821 Are you busy
189,617 Re: Forum
179,281 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9430 MB (Peak: 1.0559 MB) Zlib enabled. Server Time: 2019-01-23 03:47:26 UTC