ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#73520 12/26/06 07:44 PM
Joined: Sep 2005
Posts: 202
W
WFO Offline OP
Member
I work for a POCO where we got a complaint of "partial power". The customers' service comes off of an "underbuilt" service (where the leads from the transformer go from pole to pole and several services tap off of them).
The two services closest to the transformer have good voltage (121 on each leg to ground). At the end of the underbuilt there are four services that all are getting 114 and 126 volts.

"Aha, sez I. Classic neutral problem".

Trouble is, we check and/or redo every connection and still can't correct the problem.

As it turns out, another underbuilt from another transformer terminates on this same pole and it is not having any problems. The neutral for both services is the system neutral and is continuous between both transformers . So we transfer the end services to the other underbuilt and now that one goes from 120/120 to 114/126.

"What the ....???"

So in desperation, the serviceman starts opening the main breakers of each customer and on one, the problem suddenly goes away.
So now, with one guy off, everyone else has good voltage.

My dilemma is what do I tell this guy to fix?
Turning his main off wouldn't impact the neutral.
Any ideas?

P.S. unfortunately, nobody took any amp readings, but they're going back to get some.

Joined: Jan 2005
Posts: 109
L
Member
Check the meterbase and ground at his meter. If that is ok turn off all the breakers in the panel; turn them on one at a time till the problem shows up. Then he has a starting point. Good luck Rod

Joined: Nov 2005
Posts: 827
Likes: 1
J
Member
That sounds wierd that it would be so precisely offset with varied parallel loading of the source. The only thing that comes to mind is a chance that it could be feeding the primary of a 240/??? transformer with a fault or improper primary tap to neutral. Then you could have two center tap references fighting each other for neighborhood domination. I would expect alot of neutral current there though. I also suppose it would be possible that a damaged surge arrestor could be clamping at a reduced voltage. A scope would reveal a pretty ugly waveform if that were the case.
Joe


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5