ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 536 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#7347 01/31/02 10:12 PM
Joined: Jan 2002
Posts: 2
R
rodney2 Offline OP
Junior Member
600 A 208/120 what size and could I pair

Joined: May 2001
Posts: 176
W
Member
I assume this to be some commercial or light industrial service and that the calculations per Art 220 are in proper order. Then the lookup is in Art 310, Table 310-**, depending your application. My first guess is Table 310-16. Look down the 75 degree colume to 310Amps which is for a 350 kcMil copper cable, Type (as listed at the top of the column). Paralleling this cable brings you to 620 amps. Make temperature corrections, if required. You may use the 90 degree rating to accomplish this. Remember parallel cables must be cut to the exact same length.
YOu can use the same size neutral, or size it based on calculation in Art. 220-22.
The grounding electrode conductor is based on Table 250-66, equivalent area for parallel conductors, which would be a 2/0 copper conductor.
Hope this helps.

Joined: Nov 2000
Posts: 2,148
R
Member
Note that if the grounded conductor is sized per the Article 220 calculations that systems with very small calculated grounded conductor loads will have to comply with 250-24(b)(1) for the grounded conductor size.
Don(resqcapt19)


Don(resqcapt19)

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5