ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 8
Recent Posts
OD of Alum and Copper
by Yoopersup. 08/22/17 12:08 PM
Grid problem??
by annemarie1. 08/21/17 01:10 PM
Bathroom electrical
by doc. 08/19/17 06:53 AM
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,093 Are you busy
175,707 Re: Forum
167,918 Need opinion
Who's Online Now
1 registered members (gfretwell), 94 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#72960 - 12/12/06 09:56 PM ungrounded delta  
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
I have a 600v ungrounded delta with voltage readings of 309v,309v and and 513v phase to ground instead of the typical 347v at the sevice enterance.
Voltage phase to phase is 619v and the ground indicator light panel is Fried.
Opinions please.


Work Gear for Electricians and the Trades

#72961 - 12/12/06 10:33 PM Re: ungrounded delta  
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
Those readings have the same proportions as a high-leg delta.

Are there any single-phase distribution transformers in house? If the X0 and H0 points on such a transformer became inadvertently tied together, I think you could get that result.


#72962 - 12/12/06 11:46 PM Re: ungrounded delta  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Your readings probably mean nothing. You are probably seeing the effects of an unbalanced load on the coupling capacitance of your system. The phase to ground voltages will only be equal under balanced loading. The "better" (high impedance) your meter the more sensative it is to this effect.

You should not try to measure a voltage without a constant reference point except for historical purposes. I have seen ungrounded systems with voltages to ground as high as 2x the phase-phase voltage.


#72963 - 12/12/06 11:49 PM Re: ungrounded delta  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,104
Estero,Fl,usa
I would be curious what happened if you put a small load from line to ground. It would indicate if this was some kind of high resistance path to ground or a real bolted ground.
What kind of ground fault indication are you using?


Greg Fretwell


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7602 MB (Peak: 0.8885 MB) Zlib enabled. Server Time: 2017-08-22 16:52:42 UTC