ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Any women electricians here?
by gfretwell - 01/17/22 01:44 PM
12 Lead Motor Connection Weird
by Elektrik - 01/12/22 11:09 PM
Well There's your problem.
by gfretwell - 01/08/22 12:17 AM
Happy New Year!!
by HotLine1 - 01/04/22 09:50 AM
Sangamo s309.2
by Robski - 12/31/21 04:54 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
1 members (gfretwell), 42 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#72960 12/12/06 08:56 PM
Joined: May 2001
Posts: 376
F
frank Offline OP
Member
I have a 600v ungrounded delta with voltage readings of 309v,309v and and 513v phase to ground instead of the typical 347v at the sevice enterance.
Voltage phase to phase is 619v and the ground indicator light panel is Fried.
Opinions please.

#72961 12/12/06 09:33 PM
Joined: Sep 2003
Posts: 200
U
Member
Those readings have the same proportions as a high-leg delta.

Are there any single-phase distribution transformers in house? If the X0 and H0 points on such a transformer became inadvertently tied together, I think you could get that result.

#72962 12/12/06 10:46 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Your readings probably mean nothing. You are probably seeing the effects of an unbalanced load on the coupling capacitance of your system. The phase to ground voltages will only be equal under balanced loading. The "better" (high impedance) your meter the more sensative it is to this effect.

You should not try to measure a voltage without a constant reference point except for historical purposes. I have seen ungrounded systems with voltages to ground as high as 2x the phase-phase voltage.

#72963 12/12/06 10:49 PM
Joined: Jul 2004
Posts: 9,677
Likes: 9
G
Member
I would be curious what happened if you put a small load from line to ground. It would indicate if this was some kind of high resistance path to ground or a real bolted ground.
What kind of ground fault indication are you using?


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Top Posters(30 Days)
NORCAL 3
grich 1
Popular Topics(Views)
287,906 Are you busy
220,061 Re: Forum
206,054 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5