"AFCI" And "Did Not Trip" videos #72559
12/03/06 04:20 PM
12/03/06 04:20 PM
E
Elviscat  Offline OP
Member
Joined: Aug 2005
Posts: 214
Seattle Washington USA
I saw these two videos on YOU Tube when watching that video in the Nostalgia forum I saw these two videos;
AFCI and Not working did not trip!
note that they both appear to have been uploaded by an old well-known ECN member.
In the video two of those Motel-Room hairdryers are shown being dropped into sinks full of water, now considering the two-wire cord, and the all plastic plumbing, why would doing this trip a GFI? there'd be no path to ground, until you stuck your hand in, right? and why is the other video titled "AFCI" no AFCI's are shown, is the poster trying too say that the hairdryer-in-the-sink would've tripped an AFCI? I didn't see any arcing, nor any other reason that an AFCI would've tripped.
comments anyone?
-Will A.K.A. Elviscat

Work Gear for Electricians and the Trades
Re: "AFCI" And "Did Not Trip" videos #72560
12/03/06 05:08 PM
12/03/06 05:08 PM
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
I really hope that wasn't who I think it was doing that! [Linked Image]

I had a customer once call me to their house saying that their GFCI was no good and proceeded to attempt the same thing in front of me! (as well as convince his local Home Depot to pull all their Leviton GFCI's off the shelf) I had to explain to him that in order for the GFCI to operate their needs to be a path someplace other than back to the receptacle (like metal plumbing, your body, etc...) I advised him that the manufacturer's instructions to simply use the test and reset buttons were the most reliable way for him to check these himself...

Stuff like this floating around the internet is only going to give Henry DIY a BAD idea, in thinking he's found a superior GFCI tester! [Linked Image] Just wait until the GFCI really doesn't work and Joe Blow slips and lands his hands in the sink with the dryer [Linked Image]

Re: "AFCI" And "Did Not Trip" videos #72561
12/03/06 06:33 PM
12/03/06 06:33 PM
R
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
Hmm, I thought the GFI I see would have tripped, at least when there was water flowing into the sink. Should the flow of water from the tap (second video, steady stream, no bubbles from the tap's aerator) not provided a "grounding" path regardless if the pipes are plastic or not?

A.D

Re: "AFCI" And "Did Not Trip" videos #72562
12/03/06 06:55 PM
12/03/06 06:55 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Time for a little 'nit-picking.'

As we all knoe, there is no AFCI involved. Nor, matter of fact, is a GFI built into the hair dryer plug. I believe the correct name is "immersion curent limiting device" or some such. While, by every description I have read, this thing is supposed to operate like a GFI, it seems that the testing protocols are different somehow.

For the thing to work, water has to get into it. I notice that this did not happen in the first video until the switch was submerged. Even in the second video, water may not have actually reached any live parts.

OR - and this is certainly possible - the product had a sham device, and a counterfeit UL lable. When a foreign country supports the counterfeiting of such things, nothing short of a naval blocade will have much chance of making any difference.

Just, for the sake of argument, assume the device is legit. Having the element in the water is no sure path to current leakage; it wasn't so long ago that every coffee pot and deep fryer had immersed elements. Many still do.
Likewise, a bathroom tends to be a humid, corrosive place. I would not be surprised to find that the manufacturer had coated everything inside with a clear laquer. This would also serve as an insulator.

As I see it, things like GFI's ought to be treated like parachutes ... you do everything you can to make sure they're never needed!

(Then again, I'm old enought to remember when skydiving was dangerous .... and sex was safe! [Linked Image] )

Re: "AFCI" And "Did Not Trip" videos #72563
12/03/06 07:05 PM
12/03/06 07:05 PM
D
Dave T  Offline
Member
Joined: Jan 2005
Posts: 155
Waukesha, WI, USA
Possible all PVC plumbing with no ground path?
However, even though the water itself may not be a good conductor of current such as pure H2O, I find it very intriguing that there wouldn't be 5ma of current flowing through and path that does exist.

Re: "AFCI" And "Did Not Trip" videos #72564
12/03/06 07:06 PM
12/03/06 07:06 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Regardless of what may or may not be built in to the hairdryer, the outlet that it is plugged into is required to be GFCI protected.

That said it should not operate without a ground fault path.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: "AFCI" And "Did Not Trip" videos #72565
12/03/06 07:35 PM
12/03/06 07:35 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
Randy,
I couldn't agree more, mate!.
Things like this being on a site like Youtube, can only be bad from an electrical safety point of view.

Re: "AFCI" And "Did Not Trip" videos #72566
12/04/06 03:09 AM
12/04/06 03:09 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Maybe it's time to lobby the manufacturers for an "IFCI" (Idiot Fault Circuit Interuptor) or some sort of water sensor in the hair dryer....


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: "AFCI" And "Did Not Trip" videos #72567
12/04/06 03:22 AM
12/04/06 03:22 AM
E
Elviscat  Offline OP
Member
Joined: Aug 2005
Posts: 214
Seattle Washington USA
Rewired- I was taking a bit of a closer look at that video, and while the water's flowing the camera pans to the guy reseting the little GFI on the plug several times, and the red "on" light blinking, so I think the whatever-it-is on the cord for the dryer may have actually tripped while the water was flowing...

Re: "AFCI" And "Did Not Trip" videos #72568
12/04/06 09:48 AM
12/04/06 09:48 AM
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
Elviscat, it looks more like whoever this is, is just pressing the red button making and breaking the internal contacts himself.... the point of doing that? [Linked Image]

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,145
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,157 Are you busy
185,628 Re: Forum
174,988 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.004s) Memory: 1.0280 MB (Peak: 1.2038 MB) Zlib enabled. Server Time: 2018-07-22 04:56:57 UTC