Ansul System #71860
11/08/06 01:54 PM
11/08/06 01:54 PM
B
bot540  Offline OP
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
I am doing a commercial kitchen with an ansul system for the first time and had a few questions. The inspector want all power to the hood and exhaust fans to shut down. How is this usually acomplished, with contactors and a low voltage signal? Does anyone know where I can find wiring diagrams?
Thanks.


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Work Gear for Electricians and the Trades
Re: Ansul System #71861
11/08/06 02:20 PM
11/08/06 02:20 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The ansul panel will have electrical contacts in it, usually a few SPDT micro switches.

The most common way I handle it is by the use of shunt trip breakers controlled at 120 volts through the ansul contacts.

Be sure to find out exactly what needs to be shut down.

In my area the power to the appliances under the hood and the make up air supply shut down but exhaust fans and lights stay on.

In other areas they want all power off, before you waste time and money find out for sure what your AHJ wants.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Ansul System #71862
11/08/06 07:56 PM
11/08/06 07:56 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I agree with Bob... work closely with your fire guy on this one.

The trip mechanism will usually have two sets of contacts. One set is used in the "normally open" position by the alarm guy; the other is for you.

I use the "normally closed" contacts to interrupt power to my contactor coils. System trips, coils stop working, contactors open, stuff shuts down.

I have had the issue of the exhaust fans go both ways. The make-up air, any power under the hood, hood lights, and the gas valve (if electric- most are mechanical) all get shut off.

Usually, I will use an 8x8 gutter to mount my contactors in. I do this, as usually the power to the various items comes from different panels.

The coils really ought to be on their own dedicated circuit. This is both because it makes it easy to test the system, and you really don't want any nuisance tripping. Lose power, everything under the hood gets shut down.

As for the circuits being interrupted, I cut into them wherever it's most convenient. This could very well be at the panel, and nowhere near the appliance at all.

Re: Ansul System #71863
11/08/06 08:40 PM
11/08/06 08:40 PM
HCE727  Offline
Member
Joined: Nov 2005
Posts: 186
Delaware County, PA, USA
BOT, I have something from ANSUL, if you have a fax, I will fax it to you. E-mail me.


Hank

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,583 Are you busy
188,735 Re: Forum
178,444 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9608 MB (Peak: 1.0921 MB) Zlib enabled. Server Time: 2018-11-19 01:40:15 UTC