How long can a circcuit be? #71525
11/01/06 10:57 AM
11/01/06 10:57 AM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Another thread raised the issue of breakers not tripping. It was suggested that impedance was the cause.

So- how long can a circuit bem before impedance becomes an issue in breaker performance?

The answer seems to be available in the GEMI study. Free software, that lets you compare different solutions, is available at:
http://www.steelconduit.org/gemi.htm

Work Gear for Electricians and the Trades
Re: How long can a circcuit be? #71526
11/01/06 12:33 PM
11/01/06 12:33 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
There is no length restriction; the breakers are designed to protect the cable, which fails thermally. The instant trip is there to kill the circuit immediately if a short circuit is detected (and may not ever trip if the cable impedance is too high) but thermal trip should always work regardless of the fault circuit and protect the cables. If the breaker doesn't trip (and isn't malfunctioning), it's because it didn't see levels of fault current that would pose a danger to the building cabling, merely elevated fault current. It's not smart enough to know in-rush from a cheap compressor from a kid with a fork in the socket; AFCIs aren't even that smart. It just looks at current and trips if there's too much for too long.

On better breakers, all the trip settings are calibrated and manually configrable, so it's just a matter of taking system impedance into account when dialing in the trip settings.

[This message has been edited by SteveFehr (edited 11-01-2006).]

[This message has been edited by SteveFehr (edited 11-01-2006).]

Re: How long can a circcuit be? #71527
11/01/06 02:28 PM
11/01/06 02:28 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Steve brings up an important point. Branch overcurrent protective devices (fuses and breakers) are designed to protect the branch circuit wiring not the wiring after the receptacle.

This is a paraphrased quote from a major manufacturer concerning BOLTED short circuits:
If a low voltage phase conductor is properly sized per NEC 240, it is not possible to damage the phase conductor during short-circuits below the AIC rating of the breaker protecting the phase conductor. UL tests to verify the short-circuit rating of a circuit breaker are performed considering 75C cable. The corresponding phase conductor is sized according to the NEC and must pass the fault tests without compromising its integrity."

Re: How long can a circcuit be? #71528
11/01/06 03:33 PM
11/01/06 03:33 PM
R
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 856
Titirangi, Akld, New Zealand
Cable length is an interesting point raised here.
If a circuit is very long and the maximum load on the circuit equals the circuit braker value, the voltage at the outlet may be half the voltage and the other half of the voltage can be dissipated as heat in the cable or connection.
When motors are connected, lower voltage, less torque is available, motors may not be able to start properly and draw excessive start current adding to the problem.

Under short circuit condition the cable impedance may be high enough not to trip the braker immidiately and excessive heating in the cable may occur and possible cause of a fire.

Certainly cable length is an important fact to bear in mind.

My $0.02 worth on the topic

Regards

Raymond ( RODALCO )


The product of rotation, excitation and flux produces electricty.
Re: How long can a circcuit be? #71529
11/01/06 06:01 PM
11/01/06 06:01 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Breakers are designed and tested to protect the branch circuit conductors under all conditions. This is one of the reasons that the UL test for circuit breakers (and fuses mounted in holders) includes 4' of conductor. This way we know the conductor is protected up to the AIC rating of the device and to the thermal rating of the termination. If there is enough impedance to limit the fault current below that of the short circuit portion of the protective device then its thermal portion will protect the conductor.

Re: How long can a circcuit be? #71530
11/01/06 06:18 PM
11/01/06 06:18 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 786
Oradell NJ USA
If a cable is long enough to have enough impedance to cause its breaker not to clear a fault, is it also too long (for the gauge of wire used) for acceptable amounts of voltage drop when it's used normally? Say #14 loaded by a 13A load at the far end and the voltage drop seen by the load excessive? If you upsize the wire to get acceptable voltage drop, would this excessive impedance issue go away? Or are there issues involved if ferrious conduit or such us correctly used?

Re: How long can a circcuit be? #71531
11/01/06 07:14 PM
11/01/06 07:14 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Fault current is far in excess of normal load current, and that exacerbates voltage drop. A cable that sees 5V drop at 13A will see 50V drop at 130A. This is unrelated to normal conditions, though, where the voltage is within generally acceptable limits.

Re: How long can a circcuit be? #71532
11/01/06 07:51 PM
11/01/06 07:51 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
JBD,
Quote
If a low voltage phase conductor is properly sized per NEC 240, it is not possible to damage the phase conductor during short-circuits below the AIC rating of the breaker protecting the phase conductor.

The 1/4 cycle withstand for #14 is 3370 amps. That is below the AIC rating of all breakers.
Don


Don(resqcapt19)
Re: How long can a circcuit be? #71533
11/01/06 09:00 PM
11/01/06 09:00 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,225
Estero,Fl,usa
I think it is around 1300 feet that you could wirenut the 2 conductors of a 14ga circuit together and the breaker would never trip. You could still have good performance out there if you were just running a 100w light.
I don't know why I know this but it was either a "puzzler" or a real question on one of these BBs.


Greg Fretwell
Re: How long can a circcuit be? #71534
11/01/06 09:03 PM
11/01/06 09:03 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
Can be as long as the voltage drop allows it to be is what i always thought but i guess thats wrong.


[This message has been edited by frank (edited 11-01-2006).]

Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,967
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 7
Popular Topics(Views)
246,946 Are you busy
184,347 Re: Forum
173,548 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 1.0286 MB (Peak: 1.2065 MB) Zlib enabled. Server Time: 2018-05-28 05:11:21 UTC