Multi-wire branch circuit voltage readings #71141
10/23/06 05:20 PM
10/23/06 05:20 PM
P
poorboy  Offline OP
Member
Joined: Jun 2005
Posts: 124
Central Maine
New install in a retail store. Adjacent receptacles in a telcom room on a 12/3 MC homerun. If nothing is plugged in, you have 120 V to neutral on each circuit. If you plug in a security system transformer you have 200+ volts to neutral on the other circuit(which still has nothing plugged into it). If I unplug that and plug my 3 prong tester into the circuit I Read 176 volts to neutral on the other circuit. The condition came to light when the inspector plugged his 3 prong tester in to the second circuit with the transformer plugged into the first and saw two green lights and an orange. What am I missing here? Checked the wiring and found no problem---ckts are on different phases and share a neutral. 120 volts is derived from a transformer since this is a 480/277 service.

Work Gear for Electricians and the Trades
Re: Multi-wire branch circuit voltage readings #71142
10/23/06 05:25 PM
10/23/06 05:25 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
It really appears the neutral is not correctly wired.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Multi-wire branch circuit voltage readings #71143
10/23/06 05:57 PM
10/23/06 05:57 PM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 799
Chicago, Il.
I sure hope that your Neutral is coming from the bonded secondary center tap of that transformer.
Joe

Re: Multi-wire branch circuit voltage readings #71144
10/23/06 06:04 PM
10/23/06 06:04 PM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
I've seen very similar readings from loose or mis-wired neutrals also. That would be my first guess. Please let us know what you find out...

Re: Multi-wire branch circuit voltage readings #71145
10/24/06 03:21 PM
10/24/06 03:21 PM
P
poorboy  Offline OP
Member
Joined: Jun 2005
Posts: 124
Central Maine
Went back and looked in the panel today. The guy who made it up had the neutral from the 12/3 spliced to a piece of white THHN because it would not quite reach the neutral strip on the bottom of the panel. I followed this THHN down, across the bottom of the panel, past the neutral strip, back up the other side of the panel where it was wirenutted to the neutral tail from a GFCI breaker. Apparantly he had intended to use this piece of THHN to lengthen both neutrals so they would reach the strip. All he forgot was to CUT IT IN THE MIDDLE AND ATTACH EACH ONE TO THE NEUTRAL STRIP!!! Keep your eye on your help and never assume anything.

[This message has been edited by poorboy (edited 10-24-2006).]

Re: Multi-wire branch circuit voltage readings #71146
10/24/06 03:37 PM
10/24/06 03:37 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
LOL!!!! I shouldn't laugh, though, sounds like something I'd do!

Re: Multi-wire branch circuit voltage readings #71147
10/25/06 07:56 AM
10/25/06 07:56 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
It's amazing how much better something works if it's wired up correctly! [Linked Image]

Re: Multi-wire branch circuit voltage readings #71148
10/25/06 08:15 AM
10/25/06 08:15 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Thanks for the update poorboy. I'll keep that information in my troubleshooting brain-file...


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,181 Are you busy
189,164 Re: Forum
178,839 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.005s) Memory: 0.9930 MB (Peak: 1.1518 MB) Zlib enabled. Server Time: 2018-12-13 06:22:07 UTC