Ideal panel cover? #70482
10/09/06 10:27 AM
10/09/06 10:27 AM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
This is intended for any panel manufacturers out there.

From my point of view, the ideal panel cover would have the following features:

- First, be a size I can handle. No 36" x 76" covers;

- Second, have edges thick enough, rounded enough, that they do not act like knives if they slip, slicing my hands open;

- Be of aluminum, plastic, or other LIGHTWEIGHT material;

- Have a "foot" that supports the weight, and lines up the cover, while mounting;

- Have real handles for lifting it off; and,

- Have mounting screws of a normal thread pattern and a head that uses the same screwdriver as you use inside the panel.

One more thing: the sundry 'clamp / washer' devices some panels use, in place of screws, to hold the covers on have proven to be unreliable. Stop making them!

Work Gear for Electricians and the Trades
Re: Ideal panel cover? #70483
10/09/06 10:43 AM
10/09/06 10:43 AM
M
mahlere  Offline
Member
Joined: Nov 2005
Posts: 507
New Jersey
i'll add to that, that for service work purposes, siemens had one of the greatest covers of all time. The cover was/is hinged. Remove 3 screws and hinge the cover open, you don't even have to remove the cover. Let's you get into the guts and troubleshoot very easily.

Re: Ideal panel cover? #70484
10/09/06 07:01 PM
10/09/06 07:01 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Handles on the panel cover would be great. I get really nervous whenever I have to remove an I-Line cover that weighs alot. There's really no room for error when working with 277/ 480 voltage.

I recently got one of these surveys in an e-mail and couldn't think of thing to add to it. Oh well.

Re: Ideal panel cover? #70485
10/09/06 07:07 PM
10/09/06 07:07 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
mahlere, That is a hinge on hinge cover.

You can order them with most larger panels.

The company I work for used to provide them automatically, now only by customer spec.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Ideal panel cover? #70486
10/09/06 08:34 PM
10/09/06 08:34 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
For resi: I would say blind or SOSS hinged, and pop latched with a corner bead to blend it right into any wall. I am totally sick of discussing where it can and can not go with people who outa know better by now.

For Comm: Hinged on hinged, but with a set of screws you could transfer to also include the breaker dead front as well. Just move them over one by one for what exposure you want. Dead front on - dead front off. With it on you cant work on anything but the Gnd and Gnded bars, you need to get past the dead front to access the breakers....

Enough of covers.... Get rid of K/O's on panels I am sick and tired of them! For all the extra time I have wasted trying to gently remove one without taking out the rest, I could make my own in less time... Or just plain not being where I need them. Another waste of time. If you're installing a panel, and don't own a KO set - you have no buisiness doing it in the first place IMO. I know there are some available without them, but are fewer and farther between on availabily these days - and non-existant in many brands.

Another would be the logical placement of grounds and neutrals. One of each on each side for AF's and GF's.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Ideal panel cover? #70487
10/09/06 09:01 PM
10/09/06 09:01 PM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
e57 brings up an interesting point about the AFCIs and GFCIs needing a neutral bus near every breaker. It's looking fairly certain that the 2008 NEC is going to be implimenting a requirement for more, if not all, circuits in residential panels to be AFCI protected (as I understand it thus far).

This means that we're probably going to see most, if not all, of the panel manufacturers redesigning (or at least modifying) their products to accmodate the new requirement.

This might be a good time to start lobbying the manufacturers to make the changes we would all like to see, such as some of the great ideas on this thread.

Re: Ideal panel cover? #70488
10/09/06 09:14 PM
10/09/06 09:14 PM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
BTW, here's the thread on the new AFCI proposal...
https://www.electrical-contractor.net/ubb/Forum19/HTML/000096.html

Re: Ideal panel cover? #70489
10/09/06 09:20 PM
10/09/06 09:20 PM
M
mahlere  Offline
Member
Joined: Nov 2005
Posts: 507
New Jersey
bob, yeah I see siemens still offers them. They should be standard on all new installations [Linked Image]

or at least all new installations that I might ever have to troubleshoot at some point in time [Linked Image]

Re: Ideal panel cover? #70490
10/09/06 09:20 PM
10/09/06 09:20 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Mark,

all great points.

Quote
If you're installing a panel, and don't own a KO set - you have no business doing it in the first place


My thought as well.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Ideal panel cover? #70491
10/09/06 10:13 PM
10/09/06 10:13 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
I doubt guys who work mostly residential would agree about the KOs ;-)


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,670 Are you busy
186,403 Re: Forum
175,893 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.003s) Memory: 1.0257 MB (Peak: 1.1992 MB) Zlib enabled. Server Time: 2018-08-21 09:56:47 UTC