Today, I was working on a carrier Heat Pump. The unit was doing nothing and I suspected a fuse. I pulled the fuse and it was so hot I couldn't touch it but it tested good.

What I found was a neutral wire that had come undone. On these units, the neutral wire connects directly to one terminal of a combination fan/compressor start capacitor.

It seems that if the neutral was broken, and the ground started to carry the load, it would still not heat up the fuse.

20A fuse and the unit once fixed only drew 13A. What happened here?

Work Gear for Electricians and the Trades
Re: hot fuse on air conditioner caused by broken neutral? #6982
01/16/02 05:25 PM
01/16/02 05:25 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,275
Fullerton, CA USA
I haven't even seen a heat pump that takes a neutral. Is this a split system?
(Is the fuseholder tight?)

[This message has been edited by electure (edited 01-16-2002).]

Re: hot fuse on air conditioner caused by broken neutral? #6983
01/16/02 07:44 PM
01/16/02 07:44 PM
M
maintenanceguy  Offline OP
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
Actually, this is a PTAC unit. 277V.

All controls (t-stats, switches, etc.) switch the neutral side of all loads (compressor, fan motor, resistance heating element)so if the neutral breaks, all parts are still hot.

Re: hot fuse on air conditioner caused by broken neutral? #6984
01/16/02 08:08 PM
01/16/02 08:08 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,275
Fullerton, CA USA
Look for a U/L or another Nationally Recognized Testing Lab sticker.
Switching a neut by itself has been forbidden forever. Some of the Japanese equipt. I've run into has asked to switch both hot & neut.

Look out before you guys kill somebody!! [Linked Image]

Re: hot fuse on air conditioner caused by broken neutral? #6985
01/17/02 07:39 AM
01/17/02 07:39 AM
M
maintenanceguy  Offline OP
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
Of course switching the neutral to any appliance is not alowed, and perhaps it's not allowed by UL inside appliances either but it's something I've seen inside appliances before.

I've seen it in AC's, Commercial washers and dryers, and I don't know if I've ever seen it anywhere else or not. It's unusual but not unheard of to those of us who work inside these things alot.

Of course if you've got the power off to any of these units, you're safe. You just can't turn off the power switch on the appliance and start sticking your screwdriver inside.

Re: hot fuse on air conditioner caused by broken neutral? #6986
01/17/02 08:29 AM
01/17/02 08:29 AM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
As a maintenance electrician I've seen switched neutrals within UL approved appliances many times. It makes you wonder but there isn't a dern thing you can do about it. If you rewire the machine you've voided the UL.
To answer the question ... I only have a "what if": If the current was arching or pulsing to ground at some point near the fuse you may produce heat that is transmitted to the fuse but not necessarily through the fuse. Any signs of arcing or sparking?

Re: hot fuse on air conditioner caused by broken neutral? #6987
01/17/02 06:57 PM
01/17/02 06:57 PM
M
maintenanceguy  Offline OP
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
No sign of arcing, contact surfaces clean. The paper wrapper on the fuse was browned alittle from the heat but that was the only sign.

Once I got the machine running again, I checked the fuse a few minutes later and it had cooled off considerably.

Something was obviously not the way it was supposed to be but I was just hoping someone would say "I've see this before and..."

Oh well, some things we'll never know.

Re: hot fuse on air conditioner caused by broken neutral? #6988
01/17/02 07:42 PM
01/17/02 07:42 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
I've seen this happen a few times at 600v.The fuse element will drop into the silica and turn into a resistor.When you pull out the fuse you shake it and it becomes open.I think the last time it was a CJ 400 amp fuse.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,037
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,460 Are you busy
188,662 Re: Forum
178,362 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 14 (0.005s) Memory: 0.9946 MB (Peak: 1.1510 MB) Zlib enabled. Server Time: 2018-11-15 04:44:48 UTC