#69045 08/25/06 07:26 PM
Joined: Oct 2003
Posts: 259
J
Joey D Offline OP
Member
It seems most cabinets have no room to install the island GFI anymore. Drawers all the way to the rear and just a face on the back. Are you guys just lowering them to get them in or making the cabinet guy customize the drawer units?

#69046 08/25/06 11:22 PM
Joined: Apr 2006
Posts: 83
E
Member
Once the cabinets are on-site, the chances of getting any changes done, are usually quite rare.

You would pretty much need to drop the receptacle below the drawer box...

Only my opinion though...

#69047 08/26/06 12:49 AM
Joined: Jul 2002
Posts: 717
M
Member
Lets see, I have shortened drawers before to allow for room. Helps to have a table saw. Also I have only seen em used in my state, but take a look at a Thomas and Betts 5060 box. Very useful for surface mounting on the exterior of the cabinet. The link website says it's not UL rated but Its a UL rated box, the one in my left hand right now has a stamped UL label with a 2 hr rating. Or you could use one of those ugly old wiremold surface boxes.
http://www.acehardwareoutlet.com/(3...ails.aspx?SKU=3032125&Source=froogle

[This message has been edited by macmikeman (edited 08-26-2006).]

#69048 08/26/06 05:55 AM
Joined: Dec 2005
Posts: 64
J
Member
That box has 9.8 cu.

Three for the wires on a dead end circuit, two or the outlet. lets skip the clamps.

5 x 2.25 = 11.25

I don't think that that box is code compliant for electrical. The ul listing is probably for phone or tv.

#69049 08/26/06 06:55 AM
Joined: Dec 2003
Posts: 751
E
Member
What is wrong with simply installing plugmold under the lip of the counter?

[This message has been edited by earlydean (edited 08-26-2006).]


Earl
#69050 08/26/06 09:31 AM
Joined: Jul 2002
Posts: 717
M
Member
quote"That box has 9.8 cu.

Three for the wires on a dead end circuit, two or the outlet. lets skip the clamps.

5 x 2.25 = 11.25

I don't think that that box is code compliant for electrical. The ul listing is probably for phone or tv"

Good observation. I gave the wrong box catalog number. The right one is # 5070. 14.0 cubic inches. It has no clamps

#69051 08/26/06 10:52 PM
Joined: Jun 2006
Posts: 110
T
Member
Here in my building they 'simply' built a mini-wall behind the cabinets. Probably for the range that went all the way to the back, but it also came in handy for the electric.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
Trumpy 7
NORCAL 5
Popular Topics(Views)
300,340 Are you busy
230,001 Re: Forum
214,810 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5